Not All Drywall Contractors Are The Same. #116289
03/27/04 01:34 PM
03/27/04 01:34 PM
I
iwire  Offline OP
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I am doing the finish on a office remodel now and wanted to share a couple of pictures of the work the drywall contractor has done.

For a change it is great, and this from guys that are paid by the board not by the hour.

[Linked Image]
[Linked Image]

I have about 400 devices in this job and 99% of the drywall cut outs look like these ones.

If only it was always like this. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Tools for Electricians:
Re: Not All Drywall Contractors Are The Same. #116290
03/27/04 02:47 PM
03/27/04 02:47 PM
I
iwire  Offline OP
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
By the way, this is what it looked like before drywall.

[Linked Image]

[Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Not All Drywall Contractors Are The Same. #116291
03/27/04 05:32 PM
03/27/04 05:32 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Bob,
I don't do any cable type installations, so I have to ask about the "drip loop" in the right side stud space in the bottom picture.
Don


Don(resqcapt19)
Re: Not All Drywall Contractors Are The Same. #116292
03/27/04 06:15 PM
03/27/04 06:15 PM
I
iwire  Offline OP
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
"Drip Loop" [Linked Image] The roof is not tight. [Linked Image]

If things go the way we would like, it goes like this.

We arrive on the job before any interior walls go up.

1)Mark on floor with spray paint all electrical circuits and locations, we have a color code that identifies what it is, power, lights, HVAC, FA etc.

2)Install every bit of cable attaching it as high as possible to trusses beams and decks, leaving a coil more than long enough to reach the boxes yet to be installed.

3)Walls get built, we install all boxes.

4)Now all our guys have to do is look up and drop the previously run MC down the wall and cut into the box. The slack is already "waste" no sense of putting it in the dumpster, we use what we need in the box and work the slack back into the ceiling leaving tie wrapped coils of slack almost every where.

These come in very handy when things need to get added, as in slack to cut in a J-box.

However the wall you are looking at has a large air duct right above it, no place to leave slack, resulting in the drip loop, if we need slack it will pull up through the cable supports.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Not All Drywall Contractors Are The Same. #116293
03/28/04 08:36 AM
03/28/04 08:36 AM
P
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
I also noticed how clean the jobsite is!!
What is the one conduit run for?
Far wall box supports - very nice - how many times do we not see these installed.

Pierre


Pierre Belarge
Re: Not All Drywall Contractors Are The Same. #116294
03/28/04 09:12 AM
03/28/04 09:12 AM
I
iwire  Offline OP
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
The GC kept a very clean site and we would help to do that too. [Linked Image] [Linked Image]

Along with the obvious safety factor of a clean job site, I believe it helps the attitude (clean, professional, etc) of the workers (myself included) speeding the job along.

The pipe run is for the cabling contractor, it was part of our contract to provide 3/4" raceway up to the ceiling.

We used about 1500 cable supports and every box is a 4" sq deep with a box support.

How many of you do like we do and use 3/4" raised rings for 5/8" Sheetrock.

It makes the ring flush with the drywall and gives great support to the devices. [Linked Image]

By the way, if the walls where not going to be sound insulated with fiberglass batts we would have anti rattle clips on the MCs where they pass through the studs. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Not All Drywall Contractors Are The Same. #116295
03/28/04 09:52 AM
03/28/04 09:52 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
A very neat job!
We also use 3/4" rings on 5/8" drywall.
That extra 1/8" is actually "absorbed" by the head of the 8-32 screw tthat attaches the ring to the box.
Seems kind of costly to use deep boxes throughout, though.
What brand/type of box is that, Bob?
I see the internal cable clamps...S

Re: Not All Drywall Contractors Are The Same. #116296
03/28/04 10:28 AM
03/28/04 10:28 AM
P
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
Bob
How many electricians would be on a job like this/how long are you usually roughing a job like this? Do you ever ask for partial roughs from the inspector?

Pierre


Pierre Belarge
Re: Not All Drywall Contractors Are The Same. #116297
03/28/04 10:37 AM
03/28/04 10:37 AM
I
iwire  Offline OP
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Good Morning Scott, Thank you.

I am just a small part of a large company, the supplies are the "deal of the moment" provided by purchasing.

I ask for stock from purchasing and they shop it out.

As for the expense of deep boxes it is a non issue for us (that may change if steel keeps rising) in our market it is all about speed, the faster the better.

We have standard procedures for doing things and deep boxes are one of those, we always feed the switch so minimum 3 12/2s per switch box add to that a typical wall mount motion sensor and maybe dual switching.

By always using deep boxes the guys do not have to stop and think about box fill, you need to add a cable, go ahead and do so.

I am not saying our way is the only way, just that it works for us, employees can be rotated through different jobs and it is all the same for them.

In some ways this stinks as some guys become no more than assembly line workers, but some are happy not to have to think.

The ones that want to think get better assignments, control work, Fire Alarm running a small crew etc. [Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Not All Drywall Contractors Are The Same. #116298
03/28/04 10:52 AM
03/28/04 10:52 AM
I
iwire  Offline OP
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Pierre This area is on two floors covering about 30,000 sq ft.

I had rough wall inspection on each floor and a rough ceiling inspection on each floor.

The inspector has been out 4 times so far and will be out 2 more times for finish.

This job had 12 guys for 2 weeks to pull (about 40,000 ft MC) and box the majority of the work. During this time all the lighting feeds for the 2 x 4 troffer are also hung from the ceiling and the independent support wires for the fixtures (required in MA) are installed.

The MCs for the lights are stripped, connectors and wires nuts installed.

Bar boxes for exit signs, smoke detectors, occupancy sensors etc are also all hung from the ceiling.

All of this is done long before the grid goes in, if the job drags we will wire and hang the troffer from the support wires before the grid is installed. This is not how to make friends with the ceiling contractor though.

Once all that was done we have cut down to 5 guys to do finish work and work on cleaning up existing conditions.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Page 1 of 5 1 2 3 4 5

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,547 Are you busy
180,357 Re: Forum
170,836 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.029s Queries: 15 (0.005s) Memory: 1.0315 MB (Peak: 1.2031 MB) Zlib enabled. Server Time: 2018-01-19 15:07:46 UTC