#114204 - 02/06/03 09:47 AM Ground Down Connector  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,439
NY, USA
[Linked Image]
Quote
THIS INSPECTION WAS INTERESTING AS THE CONTRACTOR WORKED VERY HARD TO CREATE A GOOD IMPRESSION AS THE INSTALLATION WAS NEAT AND WITH THE EXCEPTION OF THE GROUND DOWN CONNECTOR (I DON'T BELIEVE IT WAS ELECTRICAL) WAS TO CODE. IF IN FACT THE CONTRACTOR HAD INSTALLED An EQUIPMENT GROUNDING CONDUCTOR INTO THE DISTRIBUTION PANEL SOME CONSIDERATION MAY HAVE BEEN MADE BUT REGARDLESS 110.3B STILL IS QUITE VISIBLE AS THE CONNECTING MEANS WAS GROUND FLUSH WITH THE MAIN DISCONNECT.


Tools for Electricians:

#114205 - 02/06/03 11:36 AM Re: Ground Down Connector  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
??????????????


#114206 - 02/06/03 11:46 AM Re: Ground Down Connector  
Scotts  Offline
Member
Joined: Jan 2002
Posts: 209
Ventura, CA, USA
I am with you Redsy, However a comment. I do not like wire ties in a panel. At some point in the future there will have to be some trouble shooting done. Then you have to cut off all the damn wire ties without nicking the insulation to find where the wire goes.

Oh yeah, nice key in the panel.

Scott


#114207 - 02/06/03 12:41 PM Re: Ground Down Connector  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
If I install ty-raps for neatness, I won't cinch them too tight. This provides wire management, while allowing enough movement to trace, remove and re-install conductors.


#114208 - 02/06/03 02:49 PM Re: Ground Down Connector  
Pearlfish  Offline
Member
Joined: Sep 2002
Posts: 83
Chicago Ridge, Il, USA
Those square Nylon thingys with the double face tape on them are guaranteed to fall off in a week.


#114209 - 02/06/03 11:04 PM Re: Ground Down Connector  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,809
Brick, NJ USA
I read this post three times, and then read the replies. Does anyone know what the "quote" under the pic means??????????
John


John

#114210 - 02/06/03 11:33 PM Re: Ground Down Connector  
txsparky  Offline
Member
Joined: May 2001
Posts: 552
Magnolia,.Texas U.S.A.
John,
It means that the pipe coming into the back of the box has been ground flush with the back of the panel and therefore has no locknut or grounding bushing so the conduit cannot serve as the ground(there is not a ground wire pulled in with the circuits.)He is saying that the fitting was not an electrical fitting so it did not meet the requirement of 110.3(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling


[This message has been edited by txsparky (edited 02-06-2003).]


Donnie

#114211 - 02/06/03 11:51 PM Re: Ground Down Connector  
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
John,

I agree. . .I can't articulate it, but when I look at the "locknut" on the "connector", I can't make sense of what I see.

I mean, this appears to be a 1" "connector" of some sort that I've never seen before. If it's been cut or ground down, it doesn't look like it was reamed.

Then there is the proximity of what appears to be concrete screw (the blue hex head) too close to the "connector" to have adequate purchase on the edge of the hole the 'connector" is in.

I need more information to interpret what I'm seeing.


Al Hildenbrand

#114212 - 02/07/03 12:44 AM Re: Ground Down Connector  
ThinkGood  Offline
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
In other words, this panel ain't grounded, right?

Is this a sub-panel?

In addition to the comments above relative to nylon ties; nylon ties also make for a very sharp corner if the extra is cut off without rounding the edges:
[Linked Image]


#114213 - 02/07/03 12:55 AM Re: Ground Down Connector  
stamcon  Offline
Member
Joined: Mar 2001
Posts: 329
So San Francisco CA
I was confused by the round "nut/washer". I think the fitting was a set screw connector that had the barrel cut off and is being used as a conduit nipple.


Page 1 of 3 1 2 3

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 15 (0.003s) Memory: 0.8186 MB (Peak: 0.9928 MB) Zlib enabled. Server Time: 2017-04-25 14:27:12 UTC