#113022 - 01/30/02 07:58 PM Remodel Box  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,458
NY, USA
[Linked Image]
Quote
This remodel box is a plastic type, cut into a kitchen cabinet, fed with a #14-3 NM-B cable which enters directly to the left of the box, as seen between the cabinet and wall. Notice 2nd open ko behind ko which has cable in it. No clamp is used.


Electrician (20 years +) is trying to use Section 370-17 (c) exception (1999 NEC) for code compliance. Any comments?


Rick Miell


Tools for Electricians:

#113023 - 01/30/02 08:29 PM Re: Remodel Box  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,262
Fullerton, CA USA
The exception applies to boxes mounted in a wall or ceiling. This isn't either. It's a cabinet.


#113024 - 01/31/02 07:54 AM Re: Remodel Box  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
I always thought this exception addressed plastic nail-on boxes which need to be stapled within 8 ".
BTW, does punching a hole in the side of an old-work box violate 110-2(b)? (99 NEC)


#113025 - 02/10/02 07:23 PM Re: Remodel Box  
Elzappr  Offline
Member
Joined: Dec 2001
Posts: 270
Oregon
Just to clear things up, the exception to 370-17(c) still requires that NM cable enters the box through a "cable knockout". From what I can see in the photo, the cable is entering through a conduit knockout.
Redsy's comment was correct..that the exception is more pertinent to the notion that you can staple the unclamped wire within 8", measured along the wire, and an exception to the usual 12" allowed in Article 336.


#113026 - 03/14/02 05:06 AM Re: Remodel Box  
seymo1  Offline
Junior Member
Joined: Mar 2002
Posts: 4
Dallas, TX USA
i don't think that is a knockout at all...just a hole drilled in the side. you can see where they failed on the first attemt.


#113027 - 03/14/02 11:21 PM Re: Remodel Box  
spkjpr  Offline
Member
Joined: Dec 2000
Posts: 218
Sedalia,MO, USA
I don't recall ever seeing any of the plastic boxes that had a conduit KO or hole in the side of the box. Could this be a possible listing violation?


#113028 - 03/15/02 07:54 PM Re: Remodel Box  
watthead  Offline
Member
Joined: Oct 2001
Posts: 172
South Carolina
what seymo said
watthead



Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.019s Queries: 14 (0.003s) Memory: 0.7835 MB (Peak: 0.9372 MB) Zlib enabled. Server Time: 2017-10-18 13:01:25 UTC