#112744 - 09/06/01 09:31 PM Hazardous Location!  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,439
NY, USA
[Linked Image]

[Linked Image]

Quote
I've been an electrician for about 16 years here in Wausau Wisconsin. The other night I was filling up my spare van with gas when I looked down and noticed this open hole in the canopy column with wires visible. After testing them with a " Volt Pen " and finding them hot decided to look in the hole for a seal-off. I found no seal-off, no ground wire, the conduit appears to be cut off and not reamed, etc... To make things better yet (not that it matters anyway but) after more investigation I found out that those wire are connected to the canopy lights at 277 volts. This station is not even 2 years old.

Craig C.



[This message has been edited by Webmaster (edited 09-06-2001).]


Tools for Electricians:

#112745 - 09/08/01 02:48 PM Re: Hazardous Location!  
johnd24  Offline
Member
Joined: Jul 2001
Posts: 62
what was the inspector smokin on that job?


#112746 - 09/10/01 10:34 PM Re: Hazardous Location!  
smokey  Offline
Member
Joined: Apr 2001
Posts: 41
cctxusa
looks like they whined and dined the inspector on that job. did u bring it to there attention??


#112747 - 09/10/01 10:48 PM Re: Hazardous Location!  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
I know there are lots of violations in this installation, but is a seal-off really required in this conduit? It is more than 18" away from the dispenser and if the conduit comes out of the ground and terminates above 18" without any type of fitting, is the seal required? I know that pits below Class 1 Div 2 areas are Class 1 Div 1, but where there is no pit, is the underground area itself classified? If so why?
Don(resqcapt19)


Don(resqcapt19)


Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.7600 MB (Peak: 0.8908 MB) Zlib enabled. Server Time: 2017-04-27 18:53:36 UTC