ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Fujifilm Recalls Power Adapter Wall Plugs
by Admin. 01/16/18 07:04 PM
VDE 0100 to introduce AFCIs
by sparky. 01/16/18 06:36 PM
Air Compressor feeder conductor sizing
by Potseal. 01/15/18 09:08 PM
Under carpet cable?
by HotLine1. 01/15/18 09:57 AM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 7 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Not Lugs #112504
06/29/01 11:06 PM
06/29/01 11:06 PM
Admin  Offline
OP
Administrator
Member
Joined: Oct 2000
Posts: 3,481
NY, USA
[Linked Image]
Quote
Here's a panel in a house only 3 years old. Note the conductors around the buss bolts, they come from the generator disco which is NOT a DPDT, only a DPST, and it feeds the whole panel... Not clearly visible are six single pole 30A breakers feeding the #12 and #14 receptacles and lights feeders.

He wanted me to put an indicator light in before the main so he could tell when the power came back on...

-Virgil

Tools for Electricians:
Re: Not Lugs #112505
06/30/01 05:40 AM
06/30/01 05:40 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,342
there is no noodle isolation here either, given a main disco before this panel.

maybe the indicator light needs to be @ the firehouse?

[Linked Image]

Re: Not Lugs #112506
06/30/01 07:35 AM
06/30/01 07:35 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,263
Fullerton, CA USA
You've sure got the haywired customers, Virgil. Did this guy explain to you his sequence of breaker flipping-switch throwing in the event of an outage? Oops would sure cause him some trouble. I think he'd be better off with a Maglite and some Coleman lanterns.

Re: Not Lugs #112507
06/30/01 04:47 PM
06/30/01 04:47 PM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
There was a homemade set of instructions on the panel cover with lots of !!!! explaining the procedure. There was a 30A 240V (not 120/240V) disco for the genny above the panel. He didn't understand when I tried to explain that the feeders between the 30A disco and the panel were hot and "protected" at 200A, only #10 wire with very bad connections... No box in the house was bonded, grounds twisted together with no connector, boxes way too small (those 45ยบ angle corner metal boxes), etc. etc. on and on... (boy I sound like a scratched record sometimes...)

He refused the work and said he'd take care of the 30A breakers himself.

How much you want to bet that they would trip 15's anyway do to overload.

How 'bout I change the subject before I become depressed?

Steve,
No main disco (back to back, kinda) so the neutral is OK...

[This message has been edited by sparky66wv (edited 06-30-2001).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,263
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,516 Are you busy
180,314 Re: Forum
170,811 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.9592 MB (Peak: 1.0898 MB) Zlib enabled. Server Time: 2018-01-17 11:06:44 UTC