Would you do this? #112433
06/21/01 07:04 AM
06/21/01 07:04 AM
Admin  Offline
OP
Administrator
Member
Joined: Oct 2000
Posts: 3,481
NY, USA
[Linked Image]

Quote
would you do this? Cadweld a #2 tinned cu to a propane tank. This was done at a cell tower site.


Submitted via Joe Tedesco

Tools for Electricians:
Re: Would you do this? #112434
06/21/01 08:53 AM
06/21/01 08:53 AM
M
Mike Wescoatt  Offline
Member
Joined: Jun 2001
Posts: 161
Cedar City, Utah
I don't deal with this type of bonding, and I'm no brain surgeon, but I'd say that is bad... I'd at least have not bonded to the pressure vessel and welded to the foot a couple of inches away.

Stand back 50' is right...


Mike Wescoatt
Re: Would you do this? #112435
06/21/01 12:07 PM
06/21/01 12:07 PM
A
Anonymous
Unregistered

Bond to all metallic objects in the vicinity. It's a metal object. It is properly bonded.

I think it is the right thing to do.

Near a radio tower static electric would be a major concern.

Not bonding a fuel tank would be a big boo-boo.

Re: Would you do this? #112436
06/21/01 04:16 PM
06/21/01 04:16 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,890
NY, USA
Mike,

I'm with you on that for sure!

Bill

Re: Would you do this? #112437
06/21/01 06:09 PM
06/21/01 06:09 PM
A
ampznvoltz  Offline
Member
Joined: Jun 2001
Posts: 9
Gretna, LA USA
Quote
Originally posted by Webmaster:
[Linked Image]

[b]Submitted via Joe Tedesco


[/B]


I would have just drilled a hole in that leg looking thing underneath the tank and put a LUG there instead. Oh and please mount that lug with a nut and bolt!!!

Re: Would you do this? #112438
06/21/01 06:46 PM
06/21/01 06:46 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,343
I'll second Joe's response, as to cad-welding a pressurized volitale vessel , they just don't make enough budwieser

[Linked Image]

Re: Would you do this? #112439
06/21/01 09:36 PM
06/21/01 09:36 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
DS,
I agree that the tank should be bonded, but it is a pressure vessel and you just can't cadweld to the vessel itself. This is most likely an ASME certified vessel and any welding to the vessel must be made by an ASME certified welder using specific procedures. I highly doubt that the cadwelding process is certified for a pressure vessel. A bolt or cadweld to the support would be fine.


Don(resqcapt19)
Re: Would you do this? #112440
06/21/01 09:40 PM
06/21/01 09:40 PM
M
Mike Wescoatt  Offline
Member
Joined: Jun 2001
Posts: 161
Cedar City, Utah
In our 1.9 million gallon pool we bond everything with a crimp on lug and thread the metal if possible and use 316 stainless bolts, 1/4" or 3/8". This allows us to remove the bond to make repairs to the equipment or the bonding strap when needed. This makes maintenance a snap... well, as snappy as it can be for over 1000 documented bonding points


Mike Wescoatt
Re: Would you do this? #112441
07/02/01 10:10 PM
07/02/01 10:10 PM
J
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
Others' comments are on the money- this is not an NEC problem, but a violation of the ASME Boiler & Pressure vessel code (and you thought the NEC was expensive!) From an engineering viewpoint, the cadweld process is hot enough to affect the temper/strength of the metal. The depth of the weld also introduces a stress riser/weak spot in the tank wall. It is also located in possibly the most vulnerable spot of the tank. Last but not least, if the tank was filled with anything -even water- at the time, the cadweld isn't even electrically sound. Another fine Darwin candidate.

Re: Would you do this? #112442
07/03/01 07:34 PM
07/03/01 07:34 PM
J
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
(Webmaster note: This may duplicate an earlier post)
This is a good example of why you should know something about other trades.
This is not an NEC violation; rather, it violates the ASME "Boiler & Pressure Vessel Code."
This job violates training, technique, materials, and certification requirements.
From an engineering viewpoint, the cadweld is hot enough to change the temper of the metal, and introduce a stress riser. It does so in one of the most vulnerable areas- on the flat, near a seam. Even if the tank was filled with water at the time, there are penetration issues.
The ground should have been attached to the tank's foot.
The installer is a Darwin candidate.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,890
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
Potseal 15
sparky 15
Popular Topics(Views)
243,565 Are you busy
180,366 Re: Forum
170,843 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.036s Queries: 14 (0.014s) Memory: 1.0073 MB (Peak: 1.1833 MB) Zlib enabled. Server Time: 2018-01-20 16:52:08 UTC