ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Single phase VS three phase generator
by 3nd4. 01/24/18 05:53 AM
AreMetal Ladders Ever OK For Electrical Work?
by HotLine1. 01/22/18 07:31 PM
Photocell
by twh. 01/22/18 05:06 PM
VDE 0100 to introduce AFCIs
by sparky. 01/20/18 05:09 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 4 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Computer rooms #11169
07/02/02 02:39 PM
07/02/02 02:39 PM
E
electrician02125  Offline OP
Member
Joined: Feb 2001
Posts: 89
Hi all,

I've been a maintenance electrician now for 10 years. About five years ago I switched over to the computer room and maintained the UPS, Mechanical, network......

Now I am responsible for the entire room up to and including osha, nfpa, nec.....

Any useful url's out there to guide me through this maze of requirements?

Work Gear for Electricians and the Trades
Re: Computer rooms #11170
07/03/02 06:41 AM
07/03/02 06:41 AM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
The first place to start is the web sites for the manufacturers of the equipment you have at your site. Then check out other UPS, PDU, static switch, generator, etc web sites to become familiar with terms and arrangements.


Ron
Re: Computer rooms #11171
07/03/02 02:21 PM
07/03/02 02:21 PM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Review Article 645 in the 2002 NEC, and NFPA 75.

Many in our industry will speak highly of the following information, available for download here:

http://www.itl.nist.gov/fipspubs/fip94.pdf


Joe Tedesco, NEC Consultant
Re: Computer rooms #11172
07/03/02 03:09 PM
07/03/02 03:09 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Joe, that is an excellent link, and bears detailed cover-to-cover study by "both camps." FIPS PUB 94 will always be a classic on perils of non-code grounding practices. It is a bit dated—for things have gotten a little better in meshing the NEC with so-called ‘technical’ / ’quiet’ / ’instrument’ / ’data-grade’ / ’isolated’ / 'flower-bed' / 'parking-lot' / 'just-plain-deadly’ grounding practices. One of the authors—Warren Lewis—will always be a hero in my book. I remember him giving a presentation at an IEEE petrochem conference about this, and he got an uncharacteristically spirited standing ovation at its conclusion.

He is a very level-headed engineer, and his message was long overdue. Believe me—he struck a deep nerve at the time. The paper served to open up a not-always-pleasant but eventually healthy dialog between tool-belt-packin’ tradesmen and computer geeks—and their seniors.


 


[This message has been edited by Bjarney (edited 07-03-2002).]

Re: Computer rooms #11173
07/03/02 03:59 PM
07/03/02 03:59 PM
J
jlhmaint  Offline
Member
Joined: May 2002
Posts: 202
Fredericktown, OH, U.S.A
the following site has links to all kinds of suppliers as well as osha, nfpa, nema, and many others i think you will like this site and want to book mark it hope this helps
http://www.electricalinfo.com/


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Popular Topics(Views)
243,607 Are you busy
180,425 Re: Forum
170,876 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.005s) Memory: 0.9669 MB (Peak: 1.1058 MB) Zlib enabled. Server Time: 2018-01-24 11:49:49 UTC