#109842 - 12/19/05 11:25 PM Upgraded Service  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
Quote
These are pics of a service I came across out in the middle of nowhere on a house that had a service call..... The panel is 200A 120/240V, with #2 THWN feeders in a 1¼" riser, and it was approved by the AHJ! [Linked Image]


Randy (Lostazhell)

[Linked Image]


[Linked Image]


[Linked Image]




[This message has been edited by electure (edited 12-19-2005).]


2017 / 2014 NEC & Related Books and Study Guides

#109843 - 12/20/05 03:26 AM Re: Upgraded Service  
Hemingray  Offline
Member
Joined: Apr 2005
Posts: 199
Lehigh Acres, FL
undersized conduit for the #2 THWN?


Cliff

#109844 - 12/20/05 12:03 PM Re: Upgraded Service  
Lostazhell  Offline
Member
Joined: Feb 2004
Posts: 1,429
Bakersfield, CA (Originally Or...
Undersized conductors for a 200A service! [Linked Image] Minimum 3/0 THWN required for this size service.


#109845 - 12/20/05 03:13 PM Re: Upgraded Service  
mxslick  Offline
Member
Joined: Oct 2004
Posts: 803
Atomic City, ID USA
Guys, to heck with the riser! [Linked Image]

How about the rat's nest of unsecured romex in that chase, the metal flex with romex in it that doesn't even connect to the panel.... [Linked Image]

I'd hate to see what's "under the hood" on this one!

Wonder what medication the AHJ was on too.... [Linked Image]


Stupid should be painful.

#109846 - 12/20/05 05:13 PM Re: Upgraded Service  
wa2ise  Offline
Member
Joined: Nov 2002
Posts: 782
Oradell NJ USA
That sticker looks to be several years old. The bad wiring probably happened after that inspection was done.


#109847 - 12/20/05 10:08 PM Re: Upgraded Service  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
I think the sticker is left over from the house it was previously installed in, somewhere else.


Mark Heller
"Well - I oughta....." -Jackie Gleason

#109848 - 12/20/05 11:55 PM Re: Upgraded Service  
Celtic  Offline
Member
Joined: Feb 2005
Posts: 361
NJ
Quote
Originally posted by Lostazhell:

Undersized conductors for a 200A service! Minimum 3/0 THWN required for this size service.


...and for that area?
See:Table 310.15(B)(6) (2002)


That is quite a mess!


[This message has been edited by Celtic (edited 12-20-2005).]


~~ CELTIC ~~
...-= NJ =-...

#109849 - 12/21/05 10:32 AM Re: Upgraded Service  
mamills  Offline
Member
Joined: Nov 2001
Posts: 745
Wharton, Texas, USA
What a quality installation!! It looks like somebody beat this thing into the wall with a sledgehammer.

A couple of questions, Randy: What's up with the black romex'es (tied in a knot)? and, what was the nature of your service call there (at this house...?)?

This thing is quite literally a "Pandora's Box".

Mike (mamills)


#109850 - 12/23/05 11:42 AM Re: Upgraded Service  
Active 1  Offline
Member
Joined: Feb 2003
Posts: 687
Grayslake IL, USA
We can't suport a drop around here with 1 1/4 RMC even if it is a 100 A service.

They want 3" RMC for 200 amp if the mast is supporting the drop.

Is this CA where the mast is on the inside wall? We allways go on the outside with the mast.

Tom


#109851 - 12/23/05 02:36 PM Re: Upgraded Service  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,211
SI,New Zealand
Just a little comment Randy.
I like the idea of that rain water deflector on the mast.


Let's face it, these days if you're not young, you're old - Red Green grin

Page 1 of 2 1 2

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,878
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 15 (0.003s) Memory: 0.8190 MB (Peak: 0.9933 MB) Zlib enabled. Server Time: 2017-05-23 20:43:39 UTC