# 12 THHN used as handle tie #109169
10/20/03 06:54 PM
10/20/03 06:54 PM
Admin  Offline
OP
Administrator
Member
Joined: Oct 2000
Posts: 3,482
NY, USA
[Linked Image]

[Linked Image]
Quote
I don't believe the wire is strong enough to trip both breakers, if suppose one of them were to trip?

-richard

2017 / 2014 NEC & Related Books and Study Guides
Re: # 12 THHN used as handle tie #109170
10/21/03 10:49 AM
10/21/03 10:49 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Handle ties are not intented to provide a common trip. They are only intended to provide a common disconnect. The code code permits "approved" handle ties in 240.20(B), but I doubt that the AHJ has approved the wire as a handle tie. Even the handle ties from the breaker manufacturer do not turn 2 breakers into a "common trip" breaker.
Don


Don(resqcapt19)
Re: # 12 THHN used as handle tie #109171
10/24/03 11:01 PM
10/24/03 11:01 PM
Admin  Offline
OP
Administrator
Member
Joined: Oct 2000
Posts: 3,482
NY, USA
Here's another Photo sent in with a question along the same lines:

[Linked Image]
Quote
Is it illegal to take two single-pole breakers and link them together with a piece of copper wire and use them as a two-pole breaker for a 220V application? Is it safety hazard? Look at breakers 7 and 9 in the power panel.

Re: # 12 THHN used as handle tie #109172
10/25/03 10:34 AM
10/25/03 10:34 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
In this second case 240.20(B) requires the use of a common trip breaker. The use of approved handle ties is not permitted for this application. If these breakers were serving a multiwire branch circuit and not a 220 volt load the use of approved handle ties would be permitted by 240.20(B)(1).
As far as a safety hazard, I don't think so. The same condition would exist if the OCPDs were fuses in place of the single pole breakers and fuses are premitted to protect this circuit.
Don
corrected my code section reference from 240.21 to 240.20

[This message has been edited by resqcapt19 (edited 10-27-2003).]


Don(resqcapt19)
Re: # 12 THHN used as handle tie #109173
10/25/03 07:23 PM
10/25/03 07:23 PM
T
ThinkGood  Offline
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
resqcapt19:

Thanks for the explanation.

Re: # 12 THHN used as handle tie #109174
10/27/03 01:14 AM
10/27/03 01:14 AM
S
sparky74  Offline
Junior Member
Joined: May 2003
Posts: 12
Naples, Italy
So for a 220V load, a two-pole breaker must be used--period! Correct?

Re: # 12 THHN used as handle tie #109175
10/27/03 07:15 AM
10/27/03 07:15 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Sparky,
Sorry, I misspoke in the earlier post. On a grounded single phase circuit the code does permit the use of single pole breakers with handle ties for 220 volt loads.
Quote
240.20(B)(B) Circuit Breaker as Overcurrent Device. Circuit breakers shall open all ungrounded conductors of the circuit unless otherwise permitted in 240.20(B)(1), (B)(2), and (B)(3).
(1) Multiwire Branch Circuit. Except where limited by 210.4(B), individual single-pole circuit breakers, with or without approved handle ties, shall be permitted as the protection for each ungrounded conductor of multiwire branch circuits that serve only single-phase line-to-neutral loads.
(2) Grounded Single-Phase and 3-wire dc Circuits. In grounded systems, individual single-pole circuit breakers with approved handle ties shall be permitted as the protection for each ungrounded conductor for line-to-line connected loads for single-phase circuits or 3-wire, direct-current circuits.


Don(resqcapt19)
Re: # 12 THHN used as handle tie #109176
10/27/03 08:45 AM
10/27/03 08:45 AM
S
sparky74  Offline
Junior Member
Joined: May 2003
Posts: 12
Naples, Italy
resqcapt19:

Thanks a lot for the info. I guess the only discrepency is that, the piece of copper wire is not an "approved" handle tie.

Re: # 12 THHN used as handle tie #109177
10/27/03 11:12 AM
10/27/03 11:12 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Sparky,
You would have to ask the AHJ about that. He can "approve" the wire if he want to.
Don


Don(resqcapt19)

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 16
Potseal 15
Popular Topics(Views)
243,589 Are you busy
180,383 Re: Forum
170,860 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 14 (0.004s) Memory: 1.0015 MB (Peak: 1.1691 MB) Zlib enabled. Server Time: 2018-01-22 08:38:26 UTC