Pool + Shower Locations #108769
01/28/04 09:32 PM
01/28/04 09:32 PM
Admin  Offline
OP
Administrator
Member
Joined: Oct 2000
Posts: 3,481
NY, USA
[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]
Quote
i have here two 'occupied' unfinished places, one is a pool with bathing suits hung off xmas lights, the other a shower in use w/o the glass door & wall.

these were taken the same day, different jobs

~Steve aka sparky

2017 / 2014 NEC & Related Books and Study Guides
Re: Pool + Shower Locations #108770
01/29/04 04:24 AM
01/29/04 04:24 AM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
That switch/receptacle box seems rather close to the shower area for my liking, even if it is a GFI outlet.

The temporary light spliced into the fixture box (last pic, upper right) is a nice touch!

Re: Pool + Shower Locations #108771
01/29/04 06:42 AM
01/29/04 06:42 AM
S
sparky  Online Content
Member
Joined: Oct 2000
Posts: 5,344
the sw/gfi location is to have a glass wall, the 3' rule will be met when it is installed.

my state (Vermont) does not have , for single family dwellings, occupancy permits.

so people tend to live with pigtails, or as situations seen here for indefinite periods of time...

where i stand as an EC here is worrisome,to energize or not energize is often the Q

~S~

Re: Pool + Shower Locations #108772
01/29/04 12:05 PM
01/29/04 12:05 PM
S
strangedog  Offline
Member
Joined: Aug 2002
Posts: 35
Dayton, Ohio
Even if the GFCI trips the wires in the open box are still hot (the line side). Don't reach for that switch from the shower or it will be the last thing you do! [Linked Image]

SD


SD
It is best for a leader to be both feared and loved. But since this usually cannot be done, it is safer to be feared.
Re: Pool + Shower Locations #108773
01/29/04 01:14 PM
01/29/04 01:14 PM
R
rmiell  Offline
Member
Joined: Nov 2000
Posts: 242
La Junta, Co. USA
What 3' rule? There is no such rule for receptacles. See Section 406.8(C). Inside the space, sure, but where does the space end? 3' out? I don't think so. The bathtub and shower space stops at the end of the bathtub (or shower floor).

Rick Miell

Re: Pool + Shower Locations #108774
01/29/04 05:54 PM
01/29/04 05:54 PM
S
sparky  Online Content
Member
Joined: Oct 2000
Posts: 5,344
Thank you Rick
i have obviously confused 550.13(F)here with a normal residency

Re: Pool + Shower Locations #108775
02/25/04 02:01 AM
02/25/04 02:01 AM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
There used to be what was refered to as the "3' rule" for outlets near sinks and the like, to be GFI'ed. It may have been re-worded, or moved in the Code. It was pretty early in the GFI requirements. I'm sure that was what Sparky was refering to, as it read very simular to that other code in motor homes.

Now get this, where I'M at... ( S.F. CA - That's right, we publish our own Code Book here, welcome to the City. And all ten Inspectors interpit it differently. ) You can get hit by the AHJ for for "within reach of the tub", to be GFI'ed. This goes for line side of a switch, sconces or fixtures below 8', and of course, outlets. ( You'll only get hit on it if it's really obvious. ) After dealing with some "San Fiasco's", you get frustrated. So, I go through this everytime I do a switch, or light near a tub. I say to myself, " F%#*, GFI the WHOLE Bathroom. At the Breakers!"

Here's another good example of a "San Fiasco":

120/240 volt 3-phase delta circuits - “A” phase black, “B” (high leg) phase PURPLE, “C” phase red;


[This message has been edited by e57 (edited 02-25-2004).]


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Pool + Shower Locations #108776
02/25/04 05:19 PM
02/25/04 05:19 PM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
Who cuts the cover plate for the switch/ receptacle?


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,576 Are you busy
180,374 Re: Forum
170,852 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.032s Queries: 14 (0.006s) Memory: 0.9934 MB (Peak: 1.1531 MB) Zlib enabled. Server Time: 2018-01-21 14:42:08 UTC