It's right there #108586
03/25/04 07:45 AM
03/25/04 07:45 AM
electure  Offline
OP
Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
It's amazing how many mistakes can be avoided by simply looking beyond one's nose.

[Linked Image]


[Linked Image]

Does anybody else have trouble with installers that simply don't pay any attention, and just "put it in"?...S

2017 / 2014 NEC & Related Books and Study Guides
Re: It's right there #108587
03/25/04 09:05 AM
03/25/04 09:05 AM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
Spooky stuff.....Its scary what we see sometimes.


Ryan Jackson,
Salt Lake City
Re: It's right there #108588
03/25/04 09:46 AM
03/25/04 09:46 AM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
Electure,

Could you elaborate on the story here?

I don't see an equipment ground conductor, and I do see the empty lugs, but I don't see enough of the box to know the the EGC is properly connected someplace else. Also, the empty lugs that I do see appear to be insulated from tbe box, and are presumably for a grounded conductor rather than the ground conductor.

Is the tape on the rightmost conductor yellow or white??? If white, I thought that the grounded conductor _could_ be switched if it was switched at the same time as the hots....

-Jon

Re: It's right there #108589
03/25/04 01:33 PM
03/25/04 01:33 PM
N
n1ist  Offline
Member
Joined: Feb 2002
Posts: 183
Malden MA
Is the cover listing 240V/225A referring to the 480V/80A breaker in the box? Does the "internal fuses" refer to the breaker above? That's not a fuse...

The color coding of brn/org/yel does jibe with the 480V breaker. The right wire is probably phase C (yel), not neutral (wht).
/mike

Re: It's right there #108590
03/25/04 02:22 PM
03/25/04 02:22 PM
J
Jim M  Offline
Member
Joined: Aug 2001
Posts: 457
Chestertown, MD, USA
The issue with the first photo is it is being used above its' voltage rating. The color code is for 277/480 3 phase and the label says 240 volts. Does the cover? look like a piece of drywall?

Re: It's right there #108591
03/25/04 04:10 PM
03/25/04 04:10 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Electure you sure make it tough. [Linked Image]

I am not sure the whole story is with picture one is.

It looks like someone installed a 480 VAC breaker in a 240 volt enclosure.

Just a note here there is no color code, brown orange yellow can be 208 volt.

With my psychic powers I will guess the second picture is a NEMA 3R disconnect mounted on a HVAC unit. For extra points I will say a unit made by Trane. [Linked Image]

This disconnect is mounted on top of a cover that needs to be opened to access fuses inside the unit.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: It's right there #108592
03/25/04 07:20 PM
03/25/04 07:20 PM
electure  Offline
OP
Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
Sorry, I didn't mean to cause any confusion.
I'll explain. [Linked Image]
Top picture = 480V 3Ø, no neutral. EGC is 1-1/4" EMT into field cut KO's (not concentrics).
The enclosure is only rated for 240V, as marked on the cover shown.

The other picture, yes he mounted it right on the panel that must remain removeable.

My "real" question was if many of you run into things like this on a regular basis, or is it just me?
The installers in both of these pictures had to look directly at the of respective labels, but apparently didn't see what was right in front of their eyes.
(Both installers read & speak English) [Linked Image]...S

[This message has been edited by electure (edited 03-25-2004).]

Re: It's right there #108593
03/25/04 10:03 PM
03/25/04 10:03 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,919
Brick, NJ USA
Electure:
Recently (doing private insp) came on a 250 volt, 200 amp (fused) disc as the primary OCP for a 480-120/208 xfr. YES it had 200 amp, 250 volt fuses, and YES it was connected to a 480 volt, 225 amp CB in the building switchboard.

Looking at the secondary....flex to a 6x6..tap to a 200 amp MCB panel (120/208) & tap to 200 amp fused disc for compressor rack. No Grd on XO, or anyplace else, except the piece of #6 ty-wrapped outside the flex, & wrapped around the flex conn screws.

A bomb waiting to blow. I guess the 'terrorists' are masquerading as 'lectricians ??? Osama Power????

John


John
Re: It's right there #108594
03/25/04 10:49 PM
03/25/04 10:49 PM
J
Jps1006  Offline
Member
Joined: Jan 2004
Posts: 615
Northern IL
we have to charge extra if you want us to think AND work at the same time.

Re: It's right there #108595
03/26/04 01:26 AM
03/26/04 01:26 AM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
 
electure—

OT a little... Didn't Challenger buy out Zinsco at one time?




[This message has been edited by Bjarney (edited 03-26-2004).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,597 Are you busy
180,402 Re: Forum
170,868 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.003s) Memory: 1.0108 MB (Peak: 1.1858 MB) Zlib enabled. Server Time: 2018-01-23 07:38:28 UTC