ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Air Compressor feeder conductor sizing
by Potseal. 01/15/18 09:08 PM
VDE 0100 to introduce AFCIs
by LongRunner. 01/15/18 11:38 AM
Under carpet cable?
by HotLine1. 01/15/18 09:57 AM
Any New Years Resolutions?
by Bill Addiss. 01/13/18 10:21 AM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 25 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 4 1 2 3 4
Will the AHJ accept this installation? #105582
05/04/05 11:52 PM
05/04/05 11:52 PM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
The Type SE grounded service entrance conductor, grounding electrode conductor and all of the equipment grounding conductors are secured to this split bolt.

The MBJ is also installed as required.

The home is still being built in the Albany, NY area and this equipment was not inspected yet?

Do you think that the AHJ will accept this concept?

The work was done by an electrician

[Linked Image]


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Will the AHJ accept this installation? #105583
05/05/05 07:26 AM
05/05/05 07:26 AM
N
NJwirenut  Offline
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
With the exception of the EGCs, this would seem to be "ugly but legal", as far as I can see. The split bolt does appear to be the required Cu/Al type, but AFAIK, split bolts are only rated for 2 conductors.

If the EGCs are moved to the neutral/ground bar where they belong, then it might have a chance of passing.

Was there no large hole available on the neutral bar to take the GEC? And it looks like the installer used his teeth to strip the GEC, as well... [Linked Image]

[This message has been edited by NJwirenut (edited 05-05-2005).]

[This message has been edited by NJwirenut (edited 05-05-2005).]

Re: Will the AHJ accept this installation? #105584
05/05/05 11:08 AM
05/05/05 11:08 AM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Here's a full view of this job.

[Linked Image]


Joe Tedesco, NEC Consultant
Re: Will the AHJ accept this installation? #105585
05/05/05 08:14 PM
05/05/05 08:14 PM
mxslick  Offline
Member
Joined: Oct 2004
Posts: 803
Atomic City, ID USA
Too rough looking, but might pass.

I think the gutter for the Romex was a good concept, but question the huge wad of wire passing thru the chase nipple (if there is one). Not as far as derating, but just to trace/locate a circuit or its breaker.

And notice all the tripped breakers? Lots of red showing!

(edited for spelling)

[This message has been edited by mxslick (edited 05-05-2005).]


Stupid should be painful.
Re: Will the AHJ accept this installation? #105586
05/06/05 11:45 PM
05/06/05 11:45 PM
S
sierra electrician  Offline
Member
Joined: Feb 2005
Posts: 219
North Fork, CA USA
No matter how you look at it, this is a "Sub Panel" and needs to have a Ground Bus insatlled. The MBJ will be at the Main where it belongs.

Rob

Re: Will the AHJ accept this installation? #105587
05/07/05 12:11 AM
05/07/05 12:11 AM
T
Tiger  Offline
Member
Joined: May 2005
Posts: 706
Crystal Lake, IL USA
I don't see why this is a sub-panel. Anyway, I see it as a violation of 250.64(C) Continuous.

Dave

Re: Will the AHJ accept this installation? #105588
05/07/05 05:32 AM
05/07/05 05:32 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Will the AHJ pass this? Who knows they very well might, there are many inspected services that use a split bolt connector in this manner.

I think the question is Should they pass this?

IMO no, the AHJ should not pass this.

Now this does not appear to me to be a sub panel.

I also do not see this as a violation of 250.64(C).

The GEC may be connected anywhere from the weatherhead to the panel.

Quote
250.24(A)(1)General.The connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.


What I do see is a 110.3(B) issue as NJwirenut was pointing out.

That split bolt connector is only listed for two conductors not a 'dozen or so'

That 'green' is not insulation, it is green tape covering all the individual EGCs for the branch circuits.

My bet is Joe is also looking for 408.20.

Quote
...Where the panelboard is used with nonmetallic raceway or cable or where separate grounding conductors are provided, a terminal bar for the grounding conductors shall be secured inside the cabinet.....


Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Will the AHJ accept this installation? #105589
05/07/05 05:48 AM
05/07/05 05:48 AM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
408.20 ... Bingo!

Also, this was the main service panel, see the MBJ "Green Screw" upper right.

[Linked Image]


Joe Tedesco, NEC Consultant
Re: Will the AHJ accept this installation? #105590
05/07/05 03:46 PM
05/07/05 03:46 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
MX...I hope the breakers are "tripped." That's how they come from the factory. (As a quality control measure, the breakers pass through a magnetic field that trips a good breaker. Those that don't trip are trashed. This is done as one of the last steps before packaging.)

Re: Will the AHJ accept this installation? #105591
05/07/05 08:26 PM
05/07/05 08:26 PM
mxslick  Offline
Member
Joined: Oct 2004
Posts: 803
Atomic City, ID USA
renosteinke:

Thanks for the info!! I had always wondered why they arrived tripped from the factory. I had thought it meant they were mishandled in shipping... [Linked Image]


Stupid should be painful.
Page 1 of 4 1 2 3 4

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 19
Potseal 13
Popular Topics(Views)
243,513 Are you busy
180,304 Re: Forum
170,802 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.084s Queries: 15 (0.017s) Memory: 1.0283 MB (Peak: 1.2040 MB) Zlib enabled. Server Time: 2018-01-16 19:26:18 UTC