Now it’s your turn to identify the violation! #105519
03/11/05 03:20 AM
03/11/05 03:20 AM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
CODE VIOLATIONS
What’s Wrong Here?

By Joe Tedesco, NEC Columnist

How well do you know the Code? Think you can spot violations the original installer either ignored or couldn’t identify himself? Here’s your chance to moonlight as an electrical inspector and second-guess someone else’s work from the safety of your living room or office. Joe Tedesco, who has a knack for finding shoddy electrical work, did the dirty work and found this mess. Now it’s your turn to identify the violation.

[Linked Image]


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Now it’s your turn to identify the violation! #105520
03/11/05 08:16 AM
03/11/05 08:16 AM
B
BOSSMAN  Offline
Member
Joined: Apr 2004
Posts: 28
BEMIDJI, MN,USA
Well the pipe should be reemed and then we need a fitting with some type of bushing.And with the looks of the conduit it might be a little tight for both of them.

Re: Now it’s your turn to identify the violation! #105521
03/11/05 02:48 PM
03/11/05 02:48 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,919
Brick, NJ USA
Joe:
A one word "What's wrong" would be EVERYTHING!
Conduit not reamed
No connector or threads/locknuts/bushing.
Excessive cable jacket within the "enclosure"
Cable installed in conduit?? (No from-to)
NO bonding of the conduit.
The 'remains' of the hole, hanging in the enclosure.
And there must be a lot more that is out of the range of your lens.
BTW, what ssize is the 'enclosure?? ..

John


John
Re: Now it’s your turn to identify the violation! #105522
03/13/05 10:07 PM
03/13/05 10:07 PM
P
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
What code violation is "excessive cable jacket" inside the enclosure?
300.10
300.15
There is a possible pipe fill violation.

Pierre


Pierre Belarge
Re: Now it’s your turn to identify the violation! #105523
03/15/05 06:18 PM
03/15/05 06:18 PM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Please continue .....

[Linked Image]

[Linked Image]


Joe Tedesco, NEC Consultant
Re: Now it’s your turn to identify the violation! #105524
03/16/05 10:07 AM
03/16/05 10:07 AM
B
BOSSMAN  Offline
Member
Joined: Apr 2004
Posts: 28
BEMIDJI, MN,USA
Well there is definity some problems here.
1.Subpanel grounds and neutrals comebined.
2.Extra set of wires in the lugs with feeders going somewere without over current protection.
3.White wire on breaker.
4.Freeder Neutral not reidentified as white.
5.Loose connection on lugs panel buned up needs replacement.
6.I hope they derated all them wires in that conduit.

Re: Now it’s your turn to identify the violation! #105525
03/16/05 07:41 PM
03/16/05 07:41 PM
G
gideonr  Offline
Member
Joined: Dec 2004
Posts: 161
Edinburgh, Scotland, UK
Insulation overstripped on a couple of wires?

Can't see it too well but what's going on in the top left corner with the knock-out possibly left open and no grommit?

Re: Now it’s your turn to identify the violation! #105526
03/24/05 01:42 PM
03/24/05 01:42 PM
R
RSmike  Offline
Member
Joined: Nov 2002
Posts: 134
Holland, MI USA
What the heck is this panel? Federal nonsPacific???

I'm just a youngin'
I've only ever seen Square D, CH, ITE, GE, Siemens.... this is new to me....or old...as the case may be.

RSlater,
RSMike

Re: Now it’s your turn to identify the violation! #105527
03/24/05 02:28 PM
03/24/05 02:28 PM
mxslick  Offline
Member
Joined: Oct 2004
Posts: 803
Atomic City, ID USA
RSmike:

That lovely panel is our old friend, Zinsco. Popular here in So Calif. along with FPE and Pushmatic. [Linked Image]


Stupid should be painful.
Re: Now it’s your turn to identify the violation! #105528
03/25/05 05:23 PM
03/25/05 05:23 PM
T
tshea  Offline
Member
Joined: Nov 2003
Posts: 16
racine, wi
I'm guessing this is actually a main service panel with NO MAIN breaker.
Zinsco or Sylvania.
I looked again. It is a main service panel.
The top 2 lugs are for the service entrance, while the 2p70 is the "lighting main" for the lower half of the panel. The top 2 pole breaker is "legal" but the 1/2 breakers in the center are not.

[This message has been edited by tshea (edited 03-25-2005).]

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,602 Are you busy
180,416 Re: Forum
170,873 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.028s Queries: 15 (0.006s) Memory: 1.0240 MB (Peak: 1.2016 MB) Zlib enabled. Server Time: 2018-01-23 21:55:38 UTC