#105484 - 02/20/05 02:34 PM Heat at termination caused a problem  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
First, let me say that I have been associated with ECN for about 3 years and have always enjoyed being involved as the person responsible for post these pictures in the forum. They are from the field and many are sent to me either here or to my email address. I also received many from readers of EC&M.

I will continue and want to thank Bill for this opportunity.

Now, let's discuss the following. Should there have been more replacements of equipment here? See any other items?

[Linked Image]

[Linked Image]


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#105485 - 02/20/05 04:49 PM Re: Heat at termination caused a problem  
mhulbert  Offline
Member
Joined: Oct 2004
Posts: 132
Anaheim, CA USA
How about 300-4(f)? Ungrounded No 4 and larger conductors enter a box, ... they shall be protected by a insulated fitting.

Also, the area around the lugs looks pretty cooked. Judging by the age of that contactor, maybe it's just from continuous loading ovewr the years? I'd put some KopperKote on them if replacement wasn't an option.


#105486 - 02/20/05 09:16 PM Re: Heat at termination caused a problem  
HLCbuild  Offline
Member
Joined: Dec 2004
Posts: 209
Herndon,Va USA
How about 200-6 Identifying the grounded conductor...continuous white or gray outer finish or 3 continuous white stripes?


#105487 - 02/20/05 10:09 PM Re: Heat at termination caused a problem  
sierra electrician  Offline
Member
Joined: Feb 2005
Posts: 219
North Fork, CA USA
I don't like the 1 Hole lugs. They look as though they could contact another phase if you were doing a PM or service because there are no dividers.

And bushings of course.

Rob


#105488 - 02/21/05 02:24 AM Re: Heat at termination caused a problem  
wa2ise  Offline
Member
Joined: Nov 2002
Posts: 782
Oradell NJ USA
At the lower right, there looks to be a mounting screw and nut behind the lower right lug. Looks like it wouldn't take much movement for the lug to short against the screw/nut. Was there some sort of block of insulation that should be used to hold the lugs more securely? I see small holes in the lugs that might have had small screws into such a block of insulation.


#105489 - 02/21/05 04:58 AM Re: Heat at termination caused a problem  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Can anyone date the work? I figure mid-late sixties... The work itself isn't bad, clean but old. I'm not sure if bushings were even required then? Didn't they make them out of lead at the time? And didn't they just realize lead caused brain damage? Speaking of metals, the lugs look to be mounted on copper clad, or other wise coated aluminum, with some sort of tin bolt covers. The lugs look copper, but with brass set-screws. Whole lotta dis-simular metals going on from the manufacturer. Maybe this was in the height of fear over use of aluminum.

Other than the bushings, I dont see anything wrong with the workmanship, just equipment failure. If this is a 3 phase contactor, the only neutral there on the coil is id'ed.


Mark Heller
"Well - I oughta....." -Jackie Gleason

#105490 - 02/21/05 09:02 PM Re: Heat at termination caused a problem  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I see heat damage to two of the lug mounts....could just be soot from cooked insulation, but I doubt it. Assuming heat damage, this could be the result of some sustained sinfle-phase operation.
I'd feel better if the starter were replaced.


#105491 - 02/21/05 10:30 PM Re: Heat at termination caused a problem  
sierra electrician  Offline
Member
Joined: Feb 2005
Posts: 219
North Fork, CA USA
After staring at this...Trying to come up with something I found a solution to saving the contactor.
1. Remove the the buss extensions.
2. Land the 1 hole lugs directly to the contactor.

This would fix any clearance issues with live an grounded parts. Like where Phase's A & C are so close to the back plate bolts.
A sheet of phenolic between the back plate & contactor would be nice.

? Is this the box that contactor came with or did someone just stuff it in Hoffman without regaurd to clearances



Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,429
Joined: February 2004