#105316 - 09/06/04 07:43 AM See anything wrong here?  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
[Linked Image]


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#105317 - 09/06/04 08:04 AM Re: See anything wrong here?  
Megawatt  Offline
Member
Joined: Mar 2004
Posts: 76
Lexington,Ky, USA
Where do You start ?? Must not own any side cutters !
Around here, I would install a Disc, & run flex to the Waterheater. Makes a nice looking installation.
Is the romex #10 ??


#105318 - 09/06/04 09:35 AM Re: See anything wrong here?  
electricman2  Offline
Member
Joined: Nov 2003
Posts: 269
Thomasville, NC USA
How could anyone walk away from this? [Linked Image]


John

#105319 - 09/06/04 09:44 AM Re: See anything wrong here?  
capt al  Offline
Member
Joined: Jun 2004
Posts: 206
Norton, Ma USA
Always nice to leave the covers off of the elements. No one would ever put their hand near there.


#105320 - 09/06/04 10:07 AM Re: See anything wrong here?  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Do we know this is complete?

The breaker can be the disconnect.

It is tough to give answers without knowing the details.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#105321 - 09/06/04 10:12 AM Re: See anything wrong here?  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Bob:

This work was what the AHJ found during the Final.

Your opinion of what you see wrong here will be appreciated.


Joe Tedesco, NEC Consultant

#105322 - 09/06/04 11:38 AM Re: See anything wrong here?  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Well if this is what it looked for the final the inspector should fail it.

The only reason I can say for sure would be lack of support of the NM 334.30 and the open cover that Capt. Al mentioned 110.27(A).

The other issues, correct wire temp rating and lack of disconnect can not be commented on from this picture alone.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#105323 - 09/06/04 11:44 AM Re: See anything wrong here?  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Bob: Discussion!

That's healthy, and that is what we do here!

I make comments all of the time to help people understand the subject of the installation.

Pictures are always helpful, but cannot show every single item.


Joe Tedesco, NEC Consultant

#105324 - 09/06/04 11:46 AM Re: See anything wrong here?  
DougW  Offline
Member
Joined: Jun 2003
Posts: 1,143
North Chicago, IL
Without knowing the conductr size, here's a quick take...

Failure to secure NM cable within appropriate distance... (336-18 '96 NEC)

Failure to secure/support NM cable @ required intervals along run...(336-18 '96 NEC)

Failure to protect NM cable from physical damage... (336-6(b) '96 NEC)

Unprotected access to equipment (failure to install in an approved manner)... (422-6 '96 NEC)


#105325 - 09/06/04 11:57 AM Re: See anything wrong here?  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Doug you are Chicago sparky right? As such you may not be used to seeing NM but it is often run exposed.

In my opinion if it was supported properly without the loop to the floor, physical damage would not be an issue at least here in MA and RI. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Page 1 of 3 1 2 3

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 15 (0.003s) Memory: 0.8176 MB (Peak: 0.9931 MB) Zlib enabled. Server Time: 2017-07-28 06:56:07 UTC