#105255 - 07/30/04 07:13 PM Mixing Line Voltage and Thermostat Wires in aAC Disconnect  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Mixing Line Voltage and Thermostat Wires in a AC Disconnect Switch.

What's the consensus? Seems to be a violation of the code?

[Linked Image]


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#105256 - 08/01/04 08:32 AM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect  
velect  Offline
Member
Joined: May 2004
Posts: 81
st joseph mi usa
Where is the ground wire to the unit

I hate it when guys ramset boxes to a wall


#105257 - 08/01/04 08:37 AM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
It was not installed!

and ... Posted: Jul 31, 2004 8:43 AM Post subject: OK!

--------------------------------------------------------------------------------

Dennis: OK, I think you done real good! and below see also the discussion on the question first posted in the link above:




The low voltage thermostat wires are not permitted to be run in the same cable or conduit because they do not have sufficient construction specifications to permit them to be installed with electric light, power conductors and any failure of the cable insulation due to a fault could lead to hazardous voltages being imposed on the thermostat circuit conductors.

The use of the same insulation for circuits up to 600 volts for both AC and DC is acceptable when run in the same cable or conduit, but not for this application.

It is better to see that thermostat wiring run in a separate cable or conduit, or wrapped around the cable or conduit that will supply the unit.


Joe Tedesco, NEC Consultant

#105258 - 08/01/04 10:12 AM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect  
SteveMc  Offline
Member
Joined: Feb 2004
Posts: 62
Rock Hill, SC
Agreed it's not a good practice, but if the wiring is all 600v rated, is it a violation? What Code reference, so I can tell the HVAC guys next time I see this done.


#105259 - 08/01/04 10:29 AM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Quote
300.3(C) Conductors of Different Systems.

(1) 600 Volts, Nominal, or Less.

Conductors of circuits rated 600 volts, nominal, or less, ac circuits, and dc circuits shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway.

All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.

Exception: For solar photovoltaic systems in accordance with 690.4(B).

FPN:See 725.55(A) for Class 2 and Class 3 circuit conductors.


Joe Tedesco, NEC Consultant

#105260 - 08/01/04 11:14 AM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect  
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
725.55 does not permit under any circumstance for Class 2 conductors to be installed in RACEWAYS with any power conductors, even associated conductors are not permitted in the same raceway.
Enclosures and other items yes, under specific restrictions, but not raceways.

Pierre


Pierre Belarge

#105261 - 08/01/04 11:46 AM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect  
Lostazhell  Offline
Member
Joined: Feb 2004
Posts: 1,431
Bakersfield, CA (Originally Or...
where is the T-stat wire gaining access to the electrical system here anyways??? It looks like its spliced into the #12TW's on the left? This is a strange installation from what I'm used to... [Linked Image]

-Randy


#105262 - 08/02/04 04:09 AM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect  
Big Jim  Offline
Member
Joined: Jul 2003
Posts: 394
Denver, CO USA
OK, the picture is not too clear to me. We have the heavy black and light blue conductor pairs that look like line and load. We have an orange and a blue spliced to the aux contacts on the breaker. And we have some sort of a coil of unidentified white wire that doesn't really seem to start or end anywhere. What's with the white - what is it? Where does it originate and terminate?


#105263 - 08/12/04 08:11 PM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect  
skingusmc  Offline
Member
Joined: May 2004
Posts: 116
Simi Valley, CA USA
The blue wire on the very left of the photo comin gout of the yellow wire nut goes up and then back down ans seems to end in a spade connector that is not attached to anything. The smaller blue wire from the same yellow worenut goes almost directly to the right and ends up in the coil of white, green, red, and yellow wire. What is going on here?


Thanks
Steve

#105264 - 08/16/04 05:40 PM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
No you can not run class 1 and 2 in the same raceway but you can reclassify class 2 or 3 circuits to class 1 then run them in the same conduit with other class 1 conductors [Linked Image] 725.52(A)Exception No. 2

I doubt highly that is the case of the wiring in Joe's Picture.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Page 1 of 2 1 2

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA