#103593 - 09/28/02 10:58 AM Hazardous (Classified) Locations, Sealing  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
[Linked Image]

Found during recent on site inspection. The seals are installed, but something is missing!

Please continue.

[This message has been edited by Joe Tedesco (edited 09-28-2002).]


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#103594 - 09/28/02 11:03 AM Re: Hazardous (Classified) Locations, Sealing  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
Oops, guess the supply house was out of wadding and "chico".
If "chico" is a regional term', it's the seal material "like cement", and "wadding" is the fiberous fill. The conductors also have to be "centered" to get a proper seal.

John


John

#103595 - 09/28/02 01:33 PM Re: Hazardous (Classified) Locations, Sealing  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
“Chico” probably stands for its manufacturer, the Crouse Hinds company. There are two parts—Chico A Sealing Compound and CHICO X Fiber.

Some hits…
Catalog description http://www.crouse-hinds.com/CrouseHinds/pdf/469.PDF
Applications: Sealing Fittings http://www.appletonelec.com/PDF/I-2-3-21.pdf

In many decades past, the ‘X-fiber’ was said to contain asbetotos wool. That has changed based on MSDS CHICO X Fiber or MSDS Chico A Sealing Compound

The ‘pour’ or proper installation is covered in 99NEC 501-5. Sealing and Drainage. (c) Class I, Divisions 1 and 2. (3) Thickness of Compounds.




[This message has been edited by Bjarney (edited 09-28-2002).]


#103596 - 09/28/02 03:47 PM Re: Hazardous (Classified) Locations, Sealing  
walrus  Offline
Member
Joined: Jul 2002
Posts: 680
Bangor Me. USA
Finally something up my alley. I see this all the time and if I'm there for an upgrade of equipment that requires me to pull wire I can't say it bothers me. It couldn't have been there to long as it is generally hard to get the plugs out after they have been in the weather awhile. I've drilled out many plugs, dug out the chico and pulled 1 wire out while pulling in several new wires many times. I generally use Duct Seal for wadding it works better than the fabric stuff. I never really thought about the listing use until I started reading this board [Linked Image]. One inspector told me that if he didn't see the sealing compound all over the outside of the sealing fitting I didn't seal it [Linked Image]

[This message has been edited by walrus (edited 09-28-2002).]


#103597 - 09/29/02 04:01 PM Re: Hazardous (Classified) Locations, Sealing  
elektrikguy  Offline
Member
Joined: May 2002
Posts: 132
woodstock,ga,usa
Doesn't look like a typical "eys" I am used to using. Is this just an older version? The ones I have used have a "fill" plug as well.


#103598 - 09/29/02 04:30 PM Re: Hazardous (Classified) Locations, Sealing  
walrus  Offline
Member
Joined: Jul 2002
Posts: 680
Bangor Me. USA
Elektrikguy

Their are several sealing fittings, the ones shown are vertical only EY-2. The ones you are refering to are Horizontal or vertical and are ENY-2. They also make one that is a 90 degree, looks kinda like a pull ell, can't remember the number.



Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.002s) Memory: 0.7774 MB (Peak: 0.9226 MB) Zlib enabled. Server Time: 2017-10-23 00:50:40 UTC