#103303 - 06/22/02 05:12 PM Bucket Used as Underground J-Box  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
This bucket was used as a junction box for some pole lights located at a hospital.

They needed power to supply an emergency entrance sign, so they notched the top of a 2 inch conduit, and then pulled the wires out to feed it!
[Linked Image]


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#103304 - 06/22/02 08:27 PM Re: Bucket Used as Underground J-Box  
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
I wonder what the maximum wire-fill would be for this ingenious junction box. I don't suppose the NEC has a table to cover it! [Linked Image]


#103305 - 06/22/02 08:49 PM Re: Bucket Used as Underground J-Box  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
It works out to 223 8-AWG THWNs for bucket fill; but reduce that to 118 for 2ΒΌ gallons of cooling water per NEC 967.229(c)II(1a)v7.


#103306 - 06/22/02 09:46 PM Re: Bucket Used as Underground J-Box  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Why didn't they remove a section of the 1.5" or 2" conduit and put two 90's on. This apears to be a quasite type box and in reality would not need an expensive divider installed. [Linked Image] If they were trying to seperate systems per 517.30(C) they crossed over anyways, not to mention being in the same raceway. The quasite box would have been legal if it were Normal, Critical, or Life Safety branches exclusively, or Normal and Equipment branches combined.

Roger



[This message has been edited by Roger (edited 06-22-2002).]


#103307 - 06/24/02 07:43 AM Re: Bucket Used as Underground J-Box  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Aha!

After 4 days of searching, the new helper finally found that "bucket of amps".



Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7685 MB (Peak: 0.9059 MB) Zlib enabled. Server Time: 2017-07-26 04:44:54 UTC