ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
Green House wiring
by gfretwell. 07/20/17 12:39 AM
1913 American Electrician's Handbook
by Admin. 07/19/17 08:41 PM
Permit Snafus...AHJs and Contractors Jump in
by HotLine1. 07/18/17 08:06 PM
210.70 / Wall Switch / When adopted?
by HotLine1. 07/16/17 11:25 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
239,163 Are you busy
174,542 Re: Forum
166,984 Need opinion
Who's Online Now
1 registered members (Potseal), 48 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#103119 - 04/09/02 10:09 PM More Working Space Violations!  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Check out the disconnect heights and working spaces.

[Linked Image]

Disconnect handles are about 7'6" from the floor.

[Linked Image]

Look at the little 60 amp disconnect to the right that is blocked by the 2 1/2" pipe in front of it!

[Linked Image]

Brian


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#103120 - 04/09/02 11:33 PM Re: More Working Space Violations!  
ZR600  Offline
Member
Joined: Apr 2002
Posts: 46
Stevens Point, WI, USA
Also check out the extension handles put on by a maint.person to aid in turning off and on the disconnects. The plant that I took the pictures at were told by their insurance company to install the handles. When you try to use them they feel like they are going to break off and in an emergency situation they may. On the 400 amp disconnect over the transformer the handle hits the top of the transformer just as it snaps to the off position but will not go far enough to allow the disconnect to be locked in the off position. With out the handle there is no way you can from the ground reach any of the disconnects with the center and right hand ones being the worst as you would have to climb on the transformer to get to them. To make matters worse workers at the plant push a large desk within a 1 1/2' of the front of the transformer. In the picture it is moved out of the way. The plant is looking at getting the original contractor in to clean this up. I have many more pictures from the same plant that I will be sending in shortly. Thanks for putting these pictures up for others to view!


#103121 - 04/10/02 07:28 AM Re: More Working Space Violations!  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Does the disconnect qualify as equipment "likely to require examination, adjustment, servicing, or maintenance while energized" ?
I would say a panelboard would require clear working space to the floor, but the disconnect may be exempt.


#103122 - 04/10/02 08:26 PM Re: More Working Space Violations!  
ZR600  Offline
Member
Joined: Apr 2002
Posts: 46
Stevens Point, WI, USA
I would site 110-26 and 380-8. Let me know if anyone sees it different. The middle (400 amp) disconnect is for the transformer that feeds a large printing press. The other two (outer two) control other stuff associated with the press. Voltage on all disconnects is 480V. Thanks


#103123 - 04/10/02 08:37 PM Re: More Working Space Violations!  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
That doesn't look like a familiar make of transformer to me but I would bet next weeks pay check that there is a line inside about 1/4 the way up that says no conduit termination's above this line. Or something to that effect.


#103124 - 04/10/02 08:46 PM Re: More Working Space Violations!  
ZR600  Offline
Member
Joined: Apr 2002
Posts: 46
Stevens Point, WI, USA
I won't take your pay check because this is a german transformer, no restriction on conduit entry on this one. The lugs are located near the top of the transformer and it has huge vents front and rear. I never saw one of these before working near german made stuff (printing industry).


#103125 - 05/26/02 08:27 PM Re: More Working Space Violations!  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Besides the clearance problem, how about the entries being above the tap lines

Roger


#103126 - 05/26/02 08:39 PM Re: More Working Space Violations!  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
I really like the tin-knockers pull can.



Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.002s) Memory: 0.7931 MB (Peak: 0.9529 MB) Zlib enabled. Server Time: 2017-07-20 12:35:48 UTC