#103041 - 03/08/02 07:38 PM Figure the Box Fill Here!  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
[Linked Image]

I would like to hear what will be said about this installation.

Is the box fill considered here where the code seems to be silent on this product?

What are these devices called?


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#103042 - 03/08/02 07:52 PM Re: Figure the Box Fill Here!  
wirewiz  Offline
Member
Joined: Jan 2002
Posts: 122
WA.
It should be considered. 370-16 4 Double volume fill allowance for the largest conducter connected to the device.


#103043 - 03/08/02 08:00 PM Re: Figure the Box Fill Here!  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,311
They are a Despard device



[This message has been edited by sparky (edited 03-11-2005).]


#103044 - 03/08/02 08:41 PM Re: Figure the Box Fill Here!  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Sparky:

The surface metal raceway extension, is the cubic inch capacity usually engraved on it?

That's what I was getting at, since it is installed over a 2 gang device box.

Thanks for the link to the Despard Devices.

Not sure about the NRTL comment, what does it mean??


Joe Tedesco, NEC Consultant

#103045 - 03/08/02 08:57 PM Re: Figure the Box Fill Here!  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,311
Joe,
most have a cu. in. marking, not sure if it's mandatory...i thought 'silent' meant box fill vs. yolk devicing... [Linked Image]

NRTL's?, well....IMO an NRTL sticker is not a mark of quality, our trade simply sees it as releasing them from liability.
This is an example of junk allowed on the market.
(my crack alluded to them on drugs..)
Fed. Pac. is another example... [Linked Image]
IC/Non-IC cans, another... [Linked Image]
I've talked to a few electricians whose AHJ's are 'breaking the sticker barrier',
shooting down 'listed' materials.
think about it!
[Linked Image]

[This message has been edited by sparky (edited 03-08-2002).]



Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,708
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7681 MB (Peak: 0.9085 MB) Zlib enabled. Server Time: 2017-10-17 15:03:41 UTC