ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
600 KW 120/208 3 Phase Y protection
by Yooperup. 07/21/17 09:27 AM
1913 American Electrician's Handbook
by gfretwell. 07/20/17 01:08 PM
Green House wiring
by ghost307. 07/20/17 09:10 AM
Permit Snafus...AHJs and Contractors Jump in
by HotLine1. 07/18/17 08:06 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
239,218 Are you busy
174,616 Re: Forum
167,042 Need opinion
Who's Online Now
0 registered members (), 62 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#102675 - 08/02/06 08:52 PM BX to motor...  
Cinner  Offline
Member
Joined: Dec 2004
Posts: 78
Kelowna, B.C., Canada
Is is right to pull a 12/3 BX wire to a 3 phase motor and use the white wire as the blue phase?

12/3 BX (red, white, black) is from a JB, which is pulled to from the panel in the right colors, to the motor, approx 8 Meters.


Tools for Electricians:

#102676 - 08/03/06 12:29 PM Re: BX to motor...  
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
You may use the white wire by making it unidentified. Paint or tabe it blue at every location the conductor is accessible.
Until the 2006 code is enacted without amendments to tables 16 and 17 you may have a problem with the bonding conductor size.

A motor conductor is sized to the FLA of the motor say it is 14 amps. The conductor size is 14 X 1.25 or 17.5 amps. A number 12 BX is OK for the motor but the potential overcurrent protection presents a challenge. If you used the max breaker size of 35 amps the bonding conductor is too small at #14. An ISO type of bx with a full sized #12 bonding conductor would take care of this. Alternately you would need a # 8 cable to meet the min #10 bonding conductor from table 16. So why can I use a #12 ISO bx and need a #8 if I use a regular BX. The bonding conductor never needs to be larger than the circuit conductor. The 2006 code sizes the bonding conductor to the wire size appropriate for the load not to the OC device protecting the load.
The cheapest solution now is ISO bx. Alternately an EMT run proximate to the motor with a short piece of flex and a #12 Bonding conductor in the flex works too. If the 2006 code is adopted without any amendments to table 16 and 17 then the #12 bx with taped or painted white wire works.



Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,878
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.7436 MB (Peak: 0.8615 MB) Zlib enabled. Server Time: 2017-07-23 00:53:25 UTC