ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
600 KW 120/208 3 Phase Y protection
by Yooperup. 07/24/17 12:20 PM
1913 American Electrician's Handbook
by gfretwell. 07/20/17 01:08 PM
Green House wiring
by ghost307. 07/20/17 09:10 AM
Permit Snafus...AHJs and Contractors Jump in
by HotLine1. 07/18/17 08:06 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
239,354 Are you busy
174,812 Re: Forum
167,196 Need opinion
Who's Online Now
0 registered members (), 86 guests, and 4 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#102481 - 04/01/06 08:26 PM Load Calculations  
teck_ed  Offline
Junior Member
Joined: Dec 2005
Posts: 6
thorold
I have a 100 amp 3 phase service commercial building. The customer wants to open a tanning salon with 4 beds. 1 is 60 amp, 220 vac, 2 @ 20 amp 220 vac and 1 is 30 amp 220 vac. Also some lights, plugs and A/C 20 amp 220 vac. Is the 100 amp 3 phase service big enough? Your help is appreciated.


Tools for Electricians:

#102482 - 04/02/06 09:46 AM Re: Load Calculations  
bigrockk  Offline
Member
Joined: Jan 2003
Posts: 174
Middle of Canada
Hello ED
Check out section 8 of the code book paying paticular attention to 8-210 and table 14.These will help you determine your service and feeder sizes.

You will need to know the outside dimensions of the building to calculate a basic load and then you will have to add in all of the "special" loads.
When determing the current draw of a paticular machine or piece of equipment make sure you check the " data plate" on the machine for this info and do not go by the breaker size it is connected to.
Hope this helps.


#102483 - 04/05/06 08:03 PM Re: Load Calculations  
marsbar  Offline
Member
Joined: Apr 2006
Posts: 31
london, ont, canada
Is you 100amp 3ph coming in at 600v? Bigrockk is right you should do a building calc. to be sure.


#102484 - 04/05/06 11:43 PM Re: Load Calculations  
bigpapa  Offline
Member
Joined: Mar 2006
Posts: 81
canada
You dont need to do any demand calculations.

The simple answer is no. Add up the KW for each load and find the total current. Its about 87A just for the beds.


#102485 - 04/06/06 08:05 AM Re: Load Calculations  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
re bigpapa's reply, you still need to refer to table 14 to establish your basic load, then as 8-210 tells us,"special loads .....based on the rating of the equipment installed with such demand factors as are permitted by this Code." Since your existing service will not be large enough, you still need to get out the calculator to determine the appropriate service feeder size.



Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 216
Joined: March 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.002s) Memory: 0.7671 MB (Peak: 0.9034 MB) Zlib enabled. Server Time: 2017-07-26 18:41:07 UTC