#102074 12/09/04 03:03 PM
Joined: Oct 2003
Posts: 172
G
Member
I,m changing an old industriul unit into three lofts.I,m using the existing incoming 600v fusible disconnect which feeds a 225kva transformer which then feeds a 800amp metering section.My question is do I need a disco in between the transformer and metering board or does the 600v main disco cover this.

#102075 12/09/04 04:11 PM
Joined: May 2001
Posts: 144
T
Moderator
The main disconnect should be fine until you get to the 800-amp 208-volt splitter.

Then you will have to install disconnect switches for each separate service, with or without utility or check meters, for the different lofts.

Tony Moscioni
Electrical Inspector
Electrical Safety Authority

#102076 12/10/04 09:29 AM
Joined: Oct 2003
Posts: 172
G
Member
Thanks Tony thats what I thought.