#101937 - 03/05/04 10:40 PM heat tape  
bill woods  Offline
Member
Joined: Nov 2001
Posts: 45
I am troubleshooting some heat tape in some eaves troughing and downspouts. The breaker keeps tripping. The tape works intermittently. It is 8W per ft 240V tape.
I can't find the fault. Anyone have experience with this stuff?


Tools for Electricians:

#101938 - 03/05/04 10:45 PM Re: heat tape  
crash  Offline
Member
Joined: Oct 2003
Posts: 147
Calgary Canada
Is it the GFCI that keeps tripping, or is it the o/c keeps tripping?


#101939 - 03/05/04 10:46 PM Re: heat tape  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,211
SI,New Zealand
There isn't a chance that the tape has been cut?.
I've seen this before with one of the wires being cut right through and only making intermittent contact.
Sounds rather dangerous actually, especially around snow!. [Linked Image]


Let's face it, these days if you're not young, you're old - Red Green grin

#101940 - 03/06/04 11:02 AM Re: heat tape  
bill woods  Offline
Member
Joined: Nov 2001
Posts: 45
There is actually two systems I'm dealing with. One is GFCI'd and the other is not. Both systems are tripping the o/c. I can't find any cuts in the cable. That is what I first suspected. Is there another way that heat tape can fail?


#101941 - 03/06/04 11:36 AM Re: heat tape  
CRM  Offline
Member
Joined: Feb 2004
Posts: 74
Alberta Canada
Is it tripping on overload or short circuit. I would measure how much current the heat tape is drawing. Somebody may have double lugged the breaker to feed another load, and now your drawing to much current.


#101942 - 03/06/04 09:14 PM Re: heat tape  
crash  Offline
Member
Joined: Oct 2003
Posts: 147
Calgary Canada
My first guess would have been a defective GFCI. My second guess would have been a fault to ground. But those posibilities have been ruled out.

The last system I installed had a small control module (to measure temperature and presence of water in the eaves troughing). The module was to be installed under the eave, I did not think the eave would provide very much protection from the weather, and the unit would probably evetually fail as a result. The other posibility is the tape is itself shorting out (maybe a break down of the insulation is causing this).


#101943 - 03/12/04 12:04 AM Re: heat tape  
twh  Offline
Member
Joined: Mar 2004
Posts: 905
Regina, Sask.
Some self-regulating heat tapes draw more current when they are cold. I measured one at three times it's rated current. The current dropped to normal in about a minute - a long enough time to trip the breaker. Check the amps when you first reset the breaker.

[This message has been edited by twh (edited 03-12-2004).]


#101944 - 03/13/04 01:40 AM Re: heat tape  
bill woods  Offline
Member
Joined: Nov 2001
Posts: 45
well i think i found the problems. one set of tapes had 120 and 240 tapes combined on the same system. the other set of tapes had water leaking into the contactor box. thank you everyone for the input.



Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.7914 MB (Peak: 0.9529 MB) Zlib enabled. Server Time: 2017-04-30 18:42:54 UTC