ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
600 KW 120/208 3 Phase Y protection
by Yooperup. 07/21/17 09:27 AM
1913 American Electrician's Handbook
by gfretwell. 07/20/17 01:08 PM
Green House wiring
by ghost307. 07/20/17 09:10 AM
Permit Snafus...AHJs and Contractors Jump in
by HotLine1. 07/18/17 08:06 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
239,229 Are you busy
174,628 Re: Forum
167,057 Need opinion
Who's Online Now
0 registered members (), 51 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#101866 - 11/06/03 10:31 PM T-Slots  
crash  Offline
Member
Joined: Oct 2003
Posts: 147
Calgary Canada
I have 2 questions:
1. If a 5-20RA receptacle was installed in full 1complience of 26-710(b), and someone was to at another date plug into this circiut a "motor-only" applience (for example a vacuum cleaner), would this violate 28-200(b)?
2. If section 14 would allow a larger overcurrent device than section 28 the which size would you choose.


Tools for Electricians:

#101867 - 11/06/03 11:34 PM Re: T-Slots  
Tony Moscioni  Offline
Moderator
Joined: May 2001
Posts: 144
CANADA
Crash,

A)No there would be no violation.

Rationale for Rule 28-200.

Because most motors have an inrush current approximately six times the motor full load current, the overcurrent device shall be of sufficient ampacity to avoid nuisance tripping.

Intent for Rule 28-200.

We intend to allow the trip values shown in Table D12, but if fuses are used and the percentage value in Table 29 will not allow the motor to start, this value may be increased. Table 26 reflects the values shown in Table 29 and is a handy guide. Appendix B provides guidance on sizing of the overcurrent protection.

B)Personally, The lower value.


#101868 - 11/08/03 04:34 PM Re: T-Slots  
crash  Offline
Member
Joined: Oct 2003
Posts: 147
Calgary Canada
Thanks, Tony.
I was thinking more along the line, that if the FLA was not known, or Table 29 indicated an over-current value of less than 14A. Then the notwithstanding clause in 28-200(b) would still allow this motor to be connected to a standard 15A receptacle supplied by a 15A O.C. . But what if a T-Slot receptacle and 20A O.C. were installed in lieu of the standard. 28-200(b) only specifies allows up to 15A.



Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.7512 MB (Peak: 0.8773 MB) Zlib enabled. Server Time: 2017-07-23 08:41:18 UTC