exit sign and emergency light hookup? #101748
02/23/03 04:29 PM
02/23/03 04:29 PM
R
RobbieD  Offline OP
Member
Joined: Feb 2003
Posts: 231
Canada
I am used to installing exit sign/emergency lighting unit combos. This time I must install an exit sign and an emergency light seperatly. Everything will be surface mounted using emt. I will be running emt from the panel to the exit sign and to a receptacle next to the lighting unit.The light unit will be plugged into it. Both will be on the same circuit and there will be nothing else in the conduit. My question is how do I supply the back up power(6VDC) from the emergency light unit to the exit sign? I want it to look nice. I don't think I can run 6Vdc in the same conduit as the 120VAC. Is the exit sign considered a remote device of the lighting unit in this case? If it is can I run the 6VDC in the same Conduit as the 120VAC if all conductors are insulated to the highest voltage rating? If not does anyone have any suggestions on how to wire it so it looks nice? Thanks

Tools for Electricians:
Re: exit sign and emergency light hookup? #101749
02/24/03 12:35 AM
02/24/03 12:35 AM
Z
ZackDitner  Offline
Member
Joined: Oct 2002
Posts: 47
Kitchener, Ontario, Canada
Hmm, usually the ones i install have backup power in each unit.. However, if you think about how you wire interconnected smokies, you use the same gauge wire for the low voltage interconnecting signal

So, I would run another wire of the same gauge and voltage rating, probably a blue or yellow wire, and use it for the backup power, does the backup require both a + & - or just one wire?

I see no code violation as long as all conductors can handle the highest voltage that will be present and conduit fill is considered

Re: exit sign and emergency light hookup? #101750
02/24/03 04:40 PM
02/24/03 04:40 PM
R
RobbieD  Offline OP
Member
Joined: Feb 2003
Posts: 231
Canada
Thanks Zack.

Re: exit sign and emergency light hookup? #101751
02/25/03 03:22 PM
02/25/03 03:22 PM
W
wdelbusto  Offline
Junior Member
Joined: Feb 2003
Posts: 3
Miami
Robbie why dont you tell us the model of light you are using it might give you a better under standing. Exit sign come is standard voltages 120v,277v even dual tap (120v/277v) so the circuit will still require one hot and a neutral and a (non-switch) for the EXIT Sign. You mentioned that the light will be Plug I dont think that a plug light is concider for life safety. Think about it if it plug it can be easily unplug and serve no purpose. now when you said plug you meant hardwire?

Regards.

Re: exit sign and emergency light hookup? #101752
02/25/03 07:13 PM
02/25/03 07:13 PM
C
CDN_ELECTRICIAN  Offline
Member
Joined: Jan 2003
Posts: 73
Concord,Ontario,Canada
Copy of post in Genaral Forum

In Ontario(If that is where your installation is) you cannot run DC & AC in same raceway.
CSA rule 46-108 (3) "Say's no WAY"

and as iwire noted NEC 700-9 (B),(1),(2),(3),(4)
Basically say's Junction Box attached to fixture (key word "attached),in fixture, and in your case Battery pack.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,602 Are you busy
180,416 Re: Forum
170,873 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.9663 MB (Peak: 1.1040 MB) Zlib enabled. Server Time: 2018-01-23 21:52:30 UTC