#101641 - 05/15/02 09:07 PM AFCI  
Lawrence  Offline
Junior Member
Joined: Nov 2001
Posts: 7
Halifax,NS,Canada
1)Will manufacturers be producing AFCI breakers for older style panels,or will there be some sort AFCI unit which can be used with older/obsolete breaker panels and/or fuse panels?


2)This is a question that was posted as a reply to another AFCI question.

I will be called upon this summer to swap out a 60amp fused panel to a 100amp breaker panel. Last summer when I was first called over to give a quote on swapping out the service they also wanted all recp's and light sw's replaced with the decora style. So I factored in gfci breakers for the upper floor bedrooms recp's which are only 2 wire circuits (no ground), this would allow me to use 3 prong outlets on ungrounded circuits with out having to try and rewire the top floor. Will these bedroom circuits require AFCI protection?

SamC


Tools for Electricians:

#101642 - 05/16/02 05:56 PM Re: AFCI  
Tony Moscioni  Offline
Moderator
Joined: May 2001
Posts: 144
CANADA
Lawrence,

1) A sub-panel might be the solution for any older type panelboards (ie; fuses, older style Commander Breaker Panels) which might not at this time, be able to support the new AFCI's.

2) In Ontario, AFCI breakers will not be required retroactively, even if the service is upgraded. They would however be required for an addition containing a bedroom.

Arc Fault Circuit Interrupters will only be required for new construction, and additions or renovations when a new circuit is provided for a bedroom. AFCI's will not be required when existing receptacles are simply replaced.

Tony Moscioni
Electrical Inspector
© Electrical Safety Authority – 2002