main breaker or not? #101171
02/14/07 11:22 AM
02/14/07 11:22 AM
R
royta  Offline OP
Member
Joined: Sep 2004
Posts: 138
CA
I've always been confused on whether I need a main breaker for a sub-panel.

Situation 1 - Residential main service with a feeder breaker feeding sub-panel mounted within or on home. Is there a situation when the sub-panel needs a main?

Situation 2 - Residential main service with a feeder breaker feeding sub-panel mounted on seperate structure or somewhere else on property. Sub-panel only needs a main IF there are more than six breaker handles (twin counts as two handles), correct?

Situation 3 - 400A residential main service with first 200A main supplying the built-in distribution. Second 200A main feeding 20/40 sub-panel located on other side of house. Sub-panel has conduit provisions to supply future sub-panels located on other structures or areas of property.

Situation 4 - Commercial main service on exterior of building. Individual feeder (main) breakers feeding sub-panels located in each commercial suite. Every sub-panel I've ever seen in these situations always has a main breaker.

[This message has been edited by royta (edited 02-14-2007).]

2017 / 2014 NEC & Related Books and Study Guides
Re: main breaker or not? #101172
02/14/07 11:49 AM
02/14/07 11:49 AM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
1. Not needed

2. Needed if six disconnects are exceeded. A 2 pole breaker is one breaker. If by twin you mean a breaker with two separate handles, then the twin counts as two.

3. Not needed

4. Not needed


Few things are harder to put up with than the annoyance of a good example.

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 20
Potseal 13
Popular Topics(Views)
243,539 Are you busy
180,341 Re: Forum
170,831 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.004s) Memory: 0.9419 MB (Peak: 1.0584 MB) Zlib enabled. Server Time: 2018-01-18 23:26:25 UTC