#10107 - 05/31/02 12:32 AM Conductors in Parallel  
arseegee  Offline
Member
Joined: Jan 2002
Posts: 324
Statesboro, GA USA
Is there a code stating the maximum number of conductors allowed to be paralleled. I know 1/0 is minimum size but found no limit on how many. I want to use four 350KCM per phase instead of two 1000KCM. Kinda tough to work that fat stuff into the bottom fed switchgear.


Work Gear for Electricians and the Trades

#10108 - 05/31/02 01:27 PM Re: Conductors in Parallel  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Four conductors per phase can be used under NEC 310-4, if the equipment is intended for 4 cdr/ø. Keep lengths equal and similarly routed for each group. If 1000kcmil is specified and there’s code-adequate bending space, use it! Won’t kill you.


#10109 - 05/31/02 05:06 PM Re: Conductors in Parallel  
Gwz  Offline
Member
Joined: Apr 2002
Posts: 197
I don't think there is a Maximum number as long at the terminations are made to accept the number of the parallel conductors.

Going from a bus to a bus I would think is virtually unlimited.

To devices such a Circuit Breakers the available (listed) lug pattern for that CB would be the determining factor.


#10110 - 05/31/02 08:40 PM Re: Conductors in Parallel  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,261
Fullerton, CA USA
I don't believe their is a maximum # of parallel conductors, as long as they meet the conditions of 310.4 ('02), or 310-4 ('99)


#10111 - 05/31/02 09:53 PM Re: Conductors in Parallel  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
I have never heard of a maximum. The more you do the harder it gets to keep them all "the same length" I have had the pleasure [said with much sarcasm] of terminating 12 runs of 500MCM paralleled myself. (And 10 runs of 600 MCM come to think of it) It is really not that bad IF you have sufficient room and you realize you are not going to finnish before lunch the day you start. (you probably won't finnish before lunch the following day either!)



Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,431
Joined: February 2004
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7680 MB (Peak: 0.9062 MB) Zlib enabled. Server Time: 2017-09-24 21:17:55 UTC