#100 - 11/25/00 01:16 PM ground wire and rods  
doc  Offline
Member
Joined: Nov 2000
Posts: 119
Texas
at a seperate building even if you run a ground with your wiring do you still have to install a ground rod at the seperate building


MAY THE SUN SHINE ON YOUR FACE IN THE MORNING AND YOU AWAKE WITH A SMILE

Work Gear for Electricians and the Trades

#101 - 11/25/00 10:25 PM Re: ground wire and rods  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
A grounding electrode system is always required at the second building unless it only has one branch circuit feeding it. See 250-32(a)
Don(resqcapt19)


Don(resqcapt19)


Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.008s Queries: 14 (0.002s) Memory: 0.7424 MB (Peak: 0.8567 MB) Zlib enabled. Server Time: 2017-07-24 22:46:25 UTC