Just drill a hole and tap a 10-32 and install a ground screw in the plastic.....................................................
Just Kidding I did work for a shop where we had a guy do just this with all the plastic nail on boxes. He spent the whole doing it. He was let go the next day. Anyway, sounds like a good install to me, unless there is a grounding tail in the fixture for the electronics.
Ob
Choose your customers, don't let them choose you.
|
|
|
|
Joined: Jul 2007
Posts: 1,335
Member
|
Just drill a hole and tap a 10-32 and install a ground screw in the plastic...
As long as the screw was green. 
Last edited by sparkyinak; 02/15/08 10:25 PM.
"Live Awesome!" - Kevin Carosa
|
|
|
|
Joined: Jul 2004
Posts: 9,795 Likes: 15
Member
|
I got the idea that the AHJ wanted the armor of the MC bonded per 314.3 and suggested it would work with a bonding bushing as per 314.3 ex2.
Greg Fretwell
|
|
|
|
Joined: Aug 2005
Posts: 251
OP
Member
|
heres an update.
I had this inspector out at this location on a different inspection and we got to talk about the MC cable and the exit/emergency light combos. I through out some big words like 'intergrated wiring compartments' and told how it is bonded at the j-box where the MC originated from just a few feet away. All he asked was if the unit was UL listed, and then said it was an 'OK' install.
Not much explination on the original violation other than he was concerned about bonding. I'm kinda thinking he wanted to meet me and let me know who the boss was....
So... MC to a 'intigrated wiring compartment' is a good install.
Shake n Bake
|
|
|
|
Joined: Jan 2005
Posts: 5,370 Likes: 1
Cat Servant Member
|
I'm glad the matter was resolved.
I've noticed the lack of a ground wire terminal on exit signs as well. I've also puzzled over the presence of a ground wire terminal on plastic junction boxes.
While some wiring methods always have a ground wire (NM, MC, etc.), you don't always need that ground wire at the end of the run. Exit signs are one such example. I think the boxes have the lug just to give you a place to tie the wire down.
|
|
|
|
Joined: Jul 2004
Posts: 9,795 Likes: 15
Member
|
I've noticed the lack of a ground wire terminal on exit signs as well. I've also puzzled over the presence of a ground wire terminal on plastic junction boxes. Is this connected to a metal mounting strap? If so, it is to bond steel framing. (a new Florida law)
Greg Fretwell
|
|
|
|
Joined: Jun 2007
Posts: 301
Member
|
Ask the inspector if he requires bonding to plastic water pipes too. He must not be very busy to call you on this one. Or he is just an idiot.
|
|
|
|
Joined: Mar 2007
Posts: 101
Member
|
You could have mounted a 4 inch square by 1 1/2 on the surface and ran EMT down to the box and mount the exit on the box.
|
|
|
Posts: 240
Joined: March 2005
|
|
|
|
|