Summer house - 09/08/06 06:50 PM
OK
Just a quick question becouse I am away from my office and can not get a hold of my 16th Regs till Monday.
Friend has just phoned (I have not seen this set up yet) he is building a summer house in his garden timber I suspect. He plans to install power via 35 Meter 10mm sq SWA.
I recon the cable would be ok
but I would like to see it supplied from a 40amp RCD to a small consumer unit in the summer house with a earth spike. ( I do not know eathing set up in his house at the moment)
Any thoughts?
Just a quick question becouse I am away from my office and can not get a hold of my 16th Regs till Monday.
Friend has just phoned (I have not seen this set up yet) he is building a summer house in his garden timber I suspect. He plans to install power via 35 Meter 10mm sq SWA.
I recon the cable would be ok
but I would like to see it supplied from a 40amp RCD to a small consumer unit in the summer house with a earth spike. ( I do not know eathing set up in his house at the moment)
Any thoughts?