Posted By: Text What is V-phase system? - 05/24/04 10:42 AM
What's the difference between 3-phase and V-phase system?Any help? I'm confused.
Posted By: Bjarney Re: What is V-phase system? - 05/24/04 04:20 PM
www.worldbank.org/html/fpd/esmap/pdfs/227_00-Grid%20Extension1.pdf
Posted By: C-H Re: What is V-phase system? - 05/24/04 04:21 PM
The latter is simply neutral plus two out of three phases.
Posted By: C-H Re: What is V-phase system? - 05/24/04 04:22 PM
Scott, you beat me to it...
Posted By: Bjarney Re: What is V-phase system? - 05/24/04 04:38 PM
Probably only by milliseconds, C-H.

;-) ;-) ;-)
Posted By: Text Re: What is V-phase system? - 07/05/04 01:02 PM
Is V-Phase other name is "open Delta"?

Can anybody show me a diagram?
Posted By: C-H Re: What is V-phase system? - 07/05/04 03:52 PM
An open delta is two transformers used to supply three phases:

In an ordinary delta, you have three single phase transformers (or one 3-phase) connected phase - to -phase. Simply remove one of the single phase transformers to create an open delta.

This means you have a limited capacity over the phase which doesn't have a transformer, but it works.

See Scotts drawings in the Reference area:
https://www.electrical-contractor.net/ubb/Forum15/HTML/000054.html

You can create something similar to V-phase by grounding one phase conductor. This is called a corner grounded delta and is sometimes used.

Homework:

Would it be possible to distribute 3-phase with only two wires and two single phase transformers (at the receiving end)? If so, how? [Linked Image]

[This message has been edited by C-H (edited 07-05-2004).]
Posted By: pauluk Re: What is V-phase system? - 07/05/04 06:48 PM
Well sure.

Someone on earth just might have grounds for wanting to do that! [Linked Image]
Posted By: Bjarney Re: What is V-phase system? - 07/05/04 11:14 PM
Another reference is Cooper Power Distribution Transformers Bulletin R201-90-2 Three Phase TRANSFORMER CONNECTIONS Compare Figure 21 – “Y-Delta With One Unit Missing “ {Also called open-wye primary} to Figure 15 – “Open Delta for Light and Power.”

See Cooperpower.com R201902.pdf