480V/3Ph/60Hz IN
OK just called My destributer technical support and got the MS coil amps. and its 8VA/120=.066666Amps.
1 - Blower Motor---------------4.5A
1 - Blower Motor Starter w/OL-- .06A(8VA)
1 - Dual Solenoid Valve---------.50A(60VA)
10 - Pilot Lights(7 max const.)--.17A
2 - Flame monitors(1A each)----2.00A
4 - Single Solenoid Valve-------.30A(10.1W each)
-------------------------------------
Total ======================7.53A(*480V=3614.4VA)
Transformer size===============3.03A(*120=363.6VA)
Is this right.?
What size fuses should i use on my main disconnect switch legs L1,L2,L3 ?
[This message has been edited by JLC (edited 12-05-2006).]
[This message has been edited by JLC (edited 12-06-2006).]
[This message has been edited by JLC (edited 12-06-2006).]
480V/3Ph/60Hz IN
OK just called My destributer technical support and got the MS coil amps. and its 8VA/120=.066666Amps.
1 - Blower Motor---------------4.5A
1 - Blower Motor Starter w/OL-- .06A(8VA)
1 - Dual Solenoid Valve---------.50A(60VA)
10 - Pilot Lights(7 max const.)--.17A
2 - Flame monitors(1A each)----2.00A
4 - Single Solenoid Valve-------.30A(10.1W each)
-------------------------------------
Total ======================7.53A(*480V=3614.4VA)
Transformer size===============3.03A(*120=363.6VA)
Is this right.?
What size fuses should i use on my main disconnect switch legs L1,L2,L3 ?