Posted By: doc LOOPS IN BOX - 05/19/01 12:11 AM
Well I have to say I have been guilty of making a complete loop in a box with bot the hot and the grounded conductor and have done it with more than one wire in the box have no idea why I stopped doing that and now just pull some extra and leave it un looped ,but have seen lots of electricains do this in the past that is where I learned it so now expand on why not to do it please
Posted By: Bill Addiss Re: LOOPS IN BOX - 05/19/01 06:36 PM
doc,

What makes you think that you can't or shouldn't leave loops in boxes? I'm just trying to understand the question.

Bill
Posted By: sparky66wv Re: LOOPS IN BOX - 05/19/01 10:56 PM
Bill,

Doc is referring to the thread here: https://www.electrical-contractor.net/ubb/Forum1/HTML/000199.html

gpowellpec has an interesting post on induction and choking that may come to play here.

-Virgil
Posted By: golf junkie Re: LOOPS IN BOX - 05/19/01 11:21 PM
gpowellpec has an interesting post on induction and choking that may come to play here.

I'm not buying that there is any appreciable inductance added to a circuit by a loop in a j-box.
If someone wants to do the math and can show that it affects breaker trip time with a fault I'll buy it.........otherwise, no way!

GJ
Posted By: Bill Addiss Re: LOOPS IN BOX - 05/19/01 11:35 PM
Thanks '66,

Didn't realize I was jumping in the middle of something here. This thread probably should have gone in the Theory section. My first thought might be that the loop wouldn't be a problem as long as the other conductors in the circuit did the same thing. I'm not sure of that though so don't jump on Me [Linked Image]

And gpowellpec did mention a spare 'conductor' in the singular so this may go along with his post also.

Bill
Posted By: doc Re: LOOPS IN BOX - 05/20/01 04:12 AM
ok Bill move it to the theory section and then give me some help on this subject LOL thanks sparky66 for grtting bill unconfused as to what i was talking about.From what I am reading this is something that could possibly happen but is not really wrong to do it or any prove of it being dangerous ? did not mean that statement as being mean or nasty just asking ?
Posted By: Bill Addiss Re: LOOPS IN BOX - 05/20/01 04:44 AM
OK,

For all that may be trying to follow this after the fact, this thread was moved to its' present location from General Area.

Scott,

Any thoughts on this?
Do you see any problems or what effect would a loop in a single conductor have and how about if all conductors had a loop?

Bill
Posted By: Scott35 Re: LOOPS IN BOX - 05/21/01 06:20 AM
Any coiled conductor carrying current will have an increased XL [Inductive Reactance], or simply a higher level of Inductance than if the conductor was run straight.
I Think that a tight loop [with a single loop coil of 1" diameter on 1 conductor], the L would be 4 times greater than straight line L.
For a 4" coil, the value might be more like 2.5 times greater than straight line [I'll need to pull out the EE books on this one, I'm just "Shooting From The Hip" here].

Now, if there's a loop with conductors carrying current that oppose each other [flow in opposite directions], that will cancel the cumilitive L on both of them, so even with many tightly wound coils, there wouldn't be a substantial increase of L in this circuit.

BTW: L = Inductance - I hate to write the entire word over and over, so luckilly we have ANSI/IEEE symbols!!

Once again, let me verify this stuff with the books and see what's up. The whole thing is equal to a single turn air coil inductor [in case you were wondering [Linked Image]], unless there are more than one turn, or there's currents flowing the opposite way.

Here's one for fun [Linked Image]:
Coil the wire for the job loop so there's like 4 layers thick and 20 stacks high, wrapped on a "Bobbin" of 1/2" GRC conduit [only one current carrying conductor].
Now run a wire through the GRC and wrap it through again and again - so it's covering the other winding.
Connect a DC source [Drycell or Battery] to the coil ran through the GRC.

?? What should happen to the AC flowing through the original coil ???

PS: Don't really do this!! Just explain what would be going on if this was done, and think of it as if you did it!
Otherwise........ Shokken Zeee Shi*zen out of ya!! could happen!!

Scott SET
Posted By: R.Legg Re: LOOPS IN BOX - 05/22/01 12:26 AM
Coiled loops take up less room. The extra wire is appreciated if the box has to be pulled temporarily from its position or have additional branches introduced at a later date.

Its not an offering made to the Electric God.
Posted By: gpowellpec Re: LOOPS IN BOX - 05/22/01 03:33 AM
If you are counting on coiling the wires of the circuit together to cancel inductances, better include the ground. If there is a short to ground that is the conductor that is going to carry the high current back to the source, not the normal "return" conductor. Anything that slows down the operation of an OCPD in a short circuit situation should be avoided. Shorts can transfer a lot of energy to the wrong place in very little time.
Posted By: Anonymous Re: LOOPS IN BOX - 05/22/01 03:43 AM
>If you are counting on coiling the wires of the circuit together to cancel inductances, better include the ground.

Uh, oh! That had better not be.


Okay, Mr. Moderator, here's the scenario.
My cable make 237 full tight loops before it gets a motor. The motor shorts out to the housing which is hooked via GRC which thanks to my careful workmanship provides a low impedance path back to the panel comparable to the grounding wire.

Now is the fault current going to be stymied by those 237 loops?
Posted By: gpowellpec Re: LOOPS IN BOX - 05/22/01 01:58 PM
Dspark,
Any way you look at it, your conductor routing has the EGC run with the ungrounded conductors and/or grounded conductor. In the tightly wrapped cable it is present inside the jacket. In the raceway it is either a conductor inside the raceway or is the raceway itself or is run on the outside of flex as allowed by NEC. If this is not so then the installation is not Code compliant. If there is a 3 phase motor being fed from cable on a wire reel and there is no EGC in the cable, there seems to be no problem as long as the inductances are being cancelled by all the current flowing in the ungrounded conductors in close proximity to each other. If there is a short to ground and the current finds a return outside of the cable the problem appears. With an EGC and other parallel paths available through conductive structures the EGC is still the lowest impedance path.
Posted By: Anonymous Re: LOOPS IN BOX - 05/22/01 08:44 PM
If there is a short to ground and the current finds a return outside of the cable the problem appears.
That is the scenario that I described.

With an EGC and other parallel paths available through conductive structures the EGC is still the lowest impedance path.

(That it is the lowest impedance path is untrue if you read the problem as I wrote it.)

Okay, I will explain the point for you and anyone else.

A lot of current will return on the conduit.
That means that the magnetic fields around the 237 loops will not be cancelled. They will act as chokes limiting the fault current.

Whether it is significant or not requires some calculation and kowledge of whether the imbalance will act as an inductor to reduce the impedance on the EGC. That's why I am hoping that Scott will answer.
Posted By: gpowellpec Re: LOOPS IN BOX - 05/22/01 10:56 PM
If fault current return path is not in close proximity to the current supplying the fault, the installation is not in compliance with 300-3(b). That requires the EGC to be in the same raceway or cable as the other circuit conductors. If the raceway is suitable for an EGC that meets the requirement. If using cable there must be an ECG in the cable if not allowed outside by 300-3(b)(2). A cable with 237 loops probably would not fall in one of the allowed conditions.
Posted By: Anonymous Re: LOOPS IN BOX - 05/23/01 12:09 AM
The NEC cannot dictate the path that fault current shall follow. If it gets to the ventilation ducts, the plumbing, or the structural steel, the OCPD had better work.

If loops (chokes) in the ungrounded conductors could pose an actual problem in such a case, then loops should be avoided. That's a big "if". And I would like to see someone who actually knows weigh in on this.
Posted By: doc Re: LOOPS IN BOX - 05/23/01 12:31 AM
I have no idea as to right or wrong here but if there is even a chance that it could be dangerous then i will make sure that i never loop again in a box ,but tell me if u want to leave extra wire in the box how would u do it ?
and remember guys try to keep theses conversations in a format that us un educated and less knowledgeable can follow
Posted By: Anonymous Re: LOOPS IN BOX - 05/23/01 12:52 AM
Loops are bad if there is another conductor going through at that might ever have a high enough voltage relative to the size of the loop.

So don't ever loop around another conductor or a metal pipe or rod.

But to make a single loop to align with a termination or such does not seem to me to be a bad thing.

As for leaving extra cable in a box, can you fold it up like ribbon candy?
Posted By: Scott35 Re: LOOPS IN BOX - 05/23/01 04:54 AM
Dspark,

Your 237 loops will be effected by ground fault current flowing through the conduit. Not that it will cancel out the total XL of the loops, but it will have some ability to reduce a field. This would be in the realm of how a Shaded Pole motor works. That consept is the reason that split phase motors can start on 1 phase AC - the "Auxillary Winding" reduces the stationary magnetic field produced by 1 phase AC on the "Run Winding", which allows the Rotor to have current Induced into it [and begin to rotate].

Back to the Q;

There's also factors on which direction the magnetic fields cross at - simply meaning is the coiled wire wound "In Step" [in 0/180 polarity], or "Out Of Step" [at 90° angles].
In step would exibit an influence on the inductor, whereas out of step will have very little effect between the two flows.
This is a topic of Breadboarding, when 2 or more Inductors are mounted on the same PCB and in close proximity. Placing them at right angles is done to reduce the amount of inductive coupling [that's why Toroids are SOOOOOO much nicer to use than normal stacked coils - the Toroids contain their fields almost entirely within themselves].

A few last things would be the diameter of the coil, permeability of the core [it's magnetic reluctance], layer depth [distance between each layer and row of coiled wire], trueness, or consistity, of the windings [AKA Perfect Layer] and finally the integrety of the coil [limited "Bouncing" between layers when currents peak or cross zero].
These factors will be used to determine the Inductance of the coil [rated in mH - milli Henrys]. Apply mH values here to obtain the XL of this coil, then apply XL to E in a simple Ohms Law Calc to find I.
If the XL looks like it would limit the I to a certain level [figure the coil's XL as a stand alone element - without the motor being in the circuit], then it would allow a level of ground fault to flow which might not be viewed as overcurrent to the OCPD.
With the motor involved in the circuit, it will create a non-stable X [XL and XC], plus R in series with the coil during normal operation - unless it is idling, or at a constant load.
Also, the motor will be contributing I during a fault [level depending on the motor's load at the time of fault]. This will change everything on the Inductor [coil], which may go as far as removing the XL created in it from the original current flow [before fault].

Scott SET

BTW: Anyone come up with anything regarding the coiled wire around the Rigid Nipple, with the DC current flowing in another coil thingee??
Posted By: Anonymous Re: LOOPS IN BOX - 05/23/01 05:31 AM
>Your 237 loops will be affected by ground fault current flowing through the conduit. Not that it will cancel out the total XL of the loops, but it will have some ability to reduce a field.
Okay, so whether the EGC is fairly parallel to the other conductors is not terribly important, right?

And if the fault current returns via a totally different path, then the loops may act as chokes and you mentioned how it could be calculated. Would you care to throw in some hard numbers as examples, like how many 2" loops to limit 100 amps or something?

>Back to the Q:
There was a request to keep "these conversations in a format that us uneducated and less knowledgeable can follow"...

>There's also factors on which direction the magnetic fields cross
So let's assume that they don't cross during a fault and they all cross during during operation.


>A few last things would be the diameter of the coil,
1 or 2"

>permeability of the core
air

>layer depth
Assume outside of pratical influence.

>trueness
perfect

>integrity of the coil
maximum

>These factors will be used to determine the Inductance of the coil
Okay, thank you. We're waiting.


>the motor will be contributing I during a fault
The fault occurred when the motor was being energized for the first time. It was not rotating and did not budge.

>Anyone come up with anything regarding the coiled wire around the Rigid Nipple, with the DC current flowing in another coil thingee??
No, but since we're trying to have fun, I'll venture that you just had me build the primary winding (AC) for a transformer whose core is the DC electromagnet. When I get near to the magnetic field, I become the secondary coil.
Posted By: Scott35 Re: LOOPS IN BOX - 05/28/01 02:29 PM
Dspark,

Sorry I haven't responded to the last post - I've been so swamped with stuff to do, I haven't been in the forums since last Wednesday or something!!
Got to run through the forums today, and man are things really happening!!!

Anyhow, I printed the thread and will throw some numbers your way ASAP. Not sure when I will be back in the forums, because this upcoming week's workload is mind-numbing!!

I do want to mention that you have obvious tech skills in advanced theory [unless you are just pulling things out of books at random [Linked Image] ...just a joke] from what I have seen here and in the Holt forum.
Have you wound your own coils [Inductors] before??
That's where I learned most of this thread's topic from - reading many-many-MANY books on the subject.

I am impressed by the many people in this forum that have such a great knowledge of the advanced areas of theory!!! You guys know who you are!! Chime in and let the people that just browse here see your names!!
If not, I will do it - and you know that will include a bunch of jokes and 100x the text needed, so it's going to be your fault!! [Linked Image]

BTW: The coil with the DC thingee is a crude example of a Magnetic Amplifier [AKA Saturable Reactor].
It's been discussed in threads before, mostly in the Holt forum between Bennie Palmer and Myself.
That was one of the first "Solid State" types of motor control, termed "Static Control Systems".
They're interresting in operation, but Jurasic in technology! [plus wasteful].

Scott SET
Posted By: Scott35 Re: LOOPS IN BOX - 06/09/01 07:10 AM
OK, Here's a few numbers on the coiled wire thingee mentioned in this thread:

For purposes of keeping things simpler, I'll use values from an one-inch air core, with multiple stacked layers. If we were to use the 2" wire coils wrapped one after another, this would create a single-layer coil, from which a tremendously long length would be needed in order to develope enough X [Reactance].
So on to the figures!! Yippee!! [Linked Image]

For a perfect layer coil, using 1" air core:
X [total Reactance] = 1.2 Ohms for 100 amps @ 120 VAC.
L [Inductance, in milli henrys "mh"] for 1.2 Ohms X = <4.0 mh - so I'll use the rounded figure of 4.0 mh

4.0 mh winding calcs for 1" perfect layer air-core coil = 20 wraps [winds], 30 layers [stacks].

These figures are only FYIs and "What-if's", since the high amperage flowing in the 4 mh coil with 120 VAC applied, will create such a high heat, there will be quite a bit more X involved from the added Resistance and Inductance. That might drop the total I down to 80 amps.

Lastly, the perfect layer calcs use varnished conductors for tight proximities in the windings and layers. Insulated conductors might affect the overall winding calc.
Also, the larger size of conductors required to pass >80 amps continuous would alter the total calc. All alterations would influence the calcs to require more windings than shown here.

Scott SET
Posted By: habbbby Re: LOOPS IN BOX - 06/09/01 10:54 PM
Interesting, its common practice when building motor control panels to loop the L leads to the motor starter for ease of amperage checks using a clamp on, it also makes a neat installation. Never heard of any reasons why NOT to do this.
Posted By: Anonymous Re: LOOPS IN BOX - 06/10/01 07:52 PM
I don't see a reason not to make a loop now and then either.

1" diameter would be a pretty tight turn for heavy wire and even if you are making 1" loops, you aren't making 600 of them in the same wire.

Scott's didn't tell you the values for a single 2" loop. But suffice it to say that it is probably comparable to having one parallel wire an inch longer than the other and no one that I know ever worries about that.

But there's a thought, folks. If you take about 1500 miles of wire and unroll it and connect both ends to the same terminal, you would have a dead short (with 60 Hz AC).

Actually, I think you might have a really bad "short" with just one end connected to the line.