250/250/200? - 04/13/05 10:06 AM
Quote
PM asked if I could take a look at a service, where she has a bid for a TI that spec’ed a 400A service.
This is part of my note back….. (She often cuts and pastes my note back to customers, that’s why its too detailed.)
The service for (That joint) in question is described as follows:
MOCP 250/250/200A (via adjustable trip setting breaker) 240V Ä 4W (Delta High Leg) w/ reduced Neutral, and High Leg Conductors (2/0 Cu TW) rated for 145A and further de-rated at 80% to 116A per 1999 NEC 310.15 (B) (2) (a), not including ambient temperature correction. Phase A, and C conductors are 350MCM Cu, with TW type insulation, rated for 260A, and further de-rated at 80% to 156A per 1999 NEC 310.15 (B) (2) (a) to 208A.
All service conductors are part of an assembly comprising 6 service disconnects tapped from a single tap section fed by parallel conductors comprised of 2 sets of service laterals of 350MCM Cu TW (700MCM) for phases A, and C, with reduced Phase B, and neutrals of 2/0 Cu TW (4/0), rated for 385A,and 195A respectively, and further de-rated at 80% per 1999 NEC 310.15 (B) (2) (a), to 308A,and 156A respectively, not including ambient temperature correction
This is part of my note back….. (She often cuts and pastes my note back to customers, that’s why its too detailed.)
The service for (That joint) in question is described as follows:
MOCP 250/250/200A (via adjustable trip setting breaker) 240V Ä 4W (Delta High Leg) w/ reduced Neutral, and High Leg Conductors (2/0 Cu TW) rated for 145A and further de-rated at 80% to 116A per 1999 NEC 310.15 (B) (2) (a), not including ambient temperature correction. Phase A, and C conductors are 350MCM Cu, with TW type insulation, rated for 260A, and further de-rated at 80% to 156A per 1999 NEC 310.15 (B) (2) (a) to 208A.
All service conductors are part of an assembly comprising 6 service disconnects tapped from a single tap section fed by parallel conductors comprised of 2 sets of service laterals of 350MCM Cu TW (700MCM) for phases A, and C, with reduced Phase B, and neutrals of 2/0 Cu TW (4/0), rated for 385A,and 195A respectively, and further de-rated at 80% per 1999 NEC 310.15 (B) (2) (a), to 308A,and 156A respectively, not including ambient temperature correction
e57