Posted By: Admin Is this legal? - 07/19/04 02:49 AM
Quote
This is an outlet installed in the side of a bathroom sink cabinet... I was always told this was not allowed...

-Randy
[Linked Image]
Posted By: ElectricAL Re: Is this legal? - 07/19/04 03:46 AM
2002 NEC
Quote
210.52 Dwelling Unit Receptacle Outlets.
(D) Bathrooms.
In dwelling units, at least one wall receptacle outlet shall be installed in bathrooms within 900 mm (3 ft) of the outside edge of each basin. The receptacle outlet shall be located on a wall or partition that is adjacent to the basin or basin countertop.
I'd take the fixed cabinet side wall as a partition.
Posted By: Lostazhell Re: Is this legal? - 07/19/04 06:25 AM
Curious thing here.... I was written up under 110.11 once for doing this..

Another curious thing,
I'm reading in the 2002 NEC Handbook in the commentary below 210.52(D),(bottom of page 91) It states:
"See 410.57(D), which prohibits installation of a receptacle inside bathtub & shower spaces."

Where the devil is 410.57???? [Linked Image]
This codebook goes from 410.54 & jumps to 410.64! I'd think it would be referring to 410.4(D), but nothing regarding receptacles is mentioned here! Anyone have any ideas?

-Randy

BTW, this outlet pictured was added by an electrician for the original builder as a "side job" after the fact. It's within 3' of the bathtub/shower also.. But my original understanding was this outlet was not allowed to be "below" the counter where if the sink overflowed, it could become wet.
Posted By: sparky Re: Is this legal? - 07/19/04 09:34 AM
if this is in 'addition to' code requirements, and outside 3', what is any different than an appliance garage rec. ??

~S~
Posted By: cpal Re: Is this legal? - 07/19/04 11:44 AM
If this receptacle is installed to conform to the requirements of 210.52 (D) the language would compel the location to be in a wall or partition. If the base cabinet is the only structural location within the 36" the AHJ could evoke 90.4.
Posted By: Joe Tedesco Re: Is this legal? - 07/19/04 12:07 PM
Randy:

410 Part L deleted and now Article 406

See 406.8 Receptacles in Damp or Wet Locations.
Posted By: WELLGROUNDED! Re: Is this legal? - 07/20/04 01:50 AM
I install many #'s inside the bath cabinet,or drawer.For hair dryers,curling irons,ect... If that plug was reversed,Would that be code?
Posted By: Lostazhell Re: Is this legal? - 07/20/04 05:06 AM
There is another outlet above the sink, out of the picture on the wall to the left....