Posted By: Admin Burnt Outlet - 05/05/04 01:38 AM
Quote
This Spec.Grade kitchen outlet and 12 ga wire were "protected" by an FPE 20 amp breaker.

Dave (aka djpep55)
[Linked Image]

[Linked Image]
Quote
Good advise from FPE:
[Linked Image]
Posted By: caselec Re: Burnt Outlet - 05/05/04 01:59 AM
I don’t think I would blame this on the breaker. The connection to the receptacle was probably loose.

Curt
Posted By: Lostazhell Re: Burnt Outlet - 05/05/04 05:38 AM
I'm with Curt on this one.... These are the same recepts I use in my work (P&S BR15W).. The pitting on the neutral wire is a giveaway of a loose terminal.. I can torque the %@%$ out of those without stripping the terminals out (Unlike Leviton, which I usually snap the head of the terminals or strip em out, By HAND!)

Possible, but unlikely... Was a shared neutral being fed through here with both hots on the same phase?

-Randy
Posted By: djpep55 Re: Burnt Outlet - 05/05/04 11:41 PM
I think you guys are right on this. I hope the fine folks of FPE can forgive me. I always wrap a solid wire around the screw and use the clamp on stranded. This had the solid wire using the clamp and as I recall it wasn't in the receptacle when I pulled it from the outlet.

Your experience is that the increase in resistance will melt the receptacle and conductor at under 20 amps?

I concur about the quality of P&S. I started using it a few years ago and never went back.

This was not fed through, it was the end of the circuit.

Dave
Posted By: Lostazhell Re: Burnt Outlet - 05/06/04 05:02 AM
djpep55 wrote:
Quote
Your experience is that the increase in resistance will melt the receptacle and conductor at under 20 amps?

with a loose connection & a load.. Absolutely!
I had a service call to a new home once.. Home was only about 3 years old... The customer almost had a fire in a kitchen receptacle.. I got there & the wall was seriously scorched, plastic 118N box melted like a shrinky-dink, recept looked like something in the back of my fireplace.. I closely examined the recept & noticed something peculiar... The terminal screws were still backed out to factory set! [Linked Image] the installer only wrapped the conductors around the screws not bothering to tighten them down!... I checked EVERY device in that house & found over half were that way! [Linked Image] [Linked Image] The load on the circuit was a 15A 120V jacuzzi plugged in the WP recept outside, which fed through here & from a counter GFI.. (Funny, I thought you weren't allowed to put other loads on the kitchen counter circuits sans the dining room or a couple other kitchen loads).. I wish I had pics from that place.. I only had a few left in my Polaroid at the time & gave them to the customer..

That was an extreme case, but I come across them alot when people start using those little "plug in" heaters..

-Randy

PS.. click here for more "burning fun" https://www.electrical-contractor.net/ubb/Forum4/HTML/000348.html
Posted By: djpep55 Re: Burnt Outlet - 05/06/04 06:12 PM
I'm glad I'm an electrician...that guy will never work on my house & another good reason for using steel boxes.

Dave
Posted By: Radar Re: Burnt Outlet - 05/06/04 06:22 PM
I've pulled out a few receptacles like this - and worse, where a good portion of the receptacle is simply gone! Circuit breakers too, and all caused by lousy connections under load.

Anyone who has any aluminum branch wire installations around their area sees this more commonly than with copper, but it still happens with copper (especially if the installer didn't even bother to tighten the stinking screws!).

Radar


[This message has been edited by Radar (edited 05-06-2004).]

[This message has been edited by Radar (edited 05-06-2004).]
Posted By: electure Re: Burnt Outlet - 05/10/04 11:49 AM
Yep, you've gotta tighten them down...S


[Linked Image]
Posted By: John Steinke Re: Burnt Outlet - 05/15/04 04:18 PM
I've seen the results of a nick in the wire insulation "plasma cutting" the neatest slot in the side of the EMT- without ever tripping a good breaker!
Visit any weld shop, and look at the settings on the machines. A LOT of welding is done with less than 2000 watts. Or, even, twenty amps.
It is very possible for a lot of melting to happen without tripping a breaker. We just don't appreciate just how much energy is available in a 20A/120V circuit.
Posted By: Electricmanscott Re: Burnt Outlet - 05/15/04 09:54 PM
djpep55, what does a steel box have to do with anything. I would be more concerned about a proper installation. If done correctly it wouldn't matter if you had no box. [Linked Image]
Posted By: Dave55 Re: Burnt Outlet - 05/25/04 12:22 AM
I was just considering the higher melting temperature of steel over plastic, Electricmanscott.

Dave
Posted By: wirenut73 Re: Burnt Outlet - 05/26/04 11:55 AM
Was that the only receptacle on that breaker?
Posted By: Dave55 Re: Burnt Outlet - 05/26/04 02:09 PM
No, Wirenut 73. It was one of three kitchen outlets. A toaster was plugged into it when it "toasted" the duplex and wire.

Dave