Posted By: Admin What's Wrong With This Picture? - 02/25/04 03:56 PM
[Linked Image]
Quote
Can anyone spot what's wrong with this picture?

PS: It's not the missing generator feed!

- Nick
Posted By: SvenNYC Re: What's Wrong With This Picture? - 02/25/04 04:23 PM
Is that black box on the cabinet door supposed to be connected to the stuff inside the cabinet via that white cable that's hanging loose in there?

That looks like some sort of multi-conductor cable for controls or something...

Also it doesn't look like it would all fit nicely together once the door is closed.... [Linked Image]
Posted By: iwire Re: What's Wrong With This Picture? - 02/25/04 04:42 PM
It looks like you have a transfer switch that uses wireless normal electricity. [Linked Image]

I hope there is no CO for this building if that is a Article 700 transfer switch.

Also I do see any control wiring for the generator.

Sven you got it, the black box is the brains of the transfer switch, most times it will have an exercise clock to run the generator on a fixed schedule

It will also have a lot of settings for different functions.

The voltage at which transfer happens.

Time delays for re transfer and cool down cycles.

As long as the harness is unplugged it will not transfer or start the engine. When the door is closed you would see a LCD display and menu buttons.

Bob

[This message has been edited by iwire (edited 02-25-2004).]
Posted By: Lostazhell Re: What's Wrong With This Picture? - 02/25/04 06:07 PM
Is that duct tape over the bottom stub to the right??
Posted By: swedejr Re: What's Wrong With This Picture? - 02/25/04 08:55 PM
Probably the generator piping....
Posted By: Nick Re: What's Wrong With This Picture? - 02/26/04 02:03 AM
The harness is unplugged and the feed from the generator is not pulled because when this picture was taken the switch was not complete. I don't have one of the finished product. There is something in the make up here that isn't right and there is an interesting story that happened because of it. I'll post tomorrow with details. [Linked Image]
Posted By: swedejr Re: What's Wrong With This Picture? - 02/26/04 09:51 PM
Do the two ground wires go to a Burndy lug? ; or does the ground wire loop from one pipe to the other?
Posted By: gunther Re: What's Wrong With This Picture? - 02/26/04 10:20 PM
Since it's been awhile since I wired a transfer switch I'm gonna make a stab at it and say the normal power is landed on the generator lugs?
Posted By: Bjarney Re: What's Wrong With This Picture? - 02/26/04 11:26 PM
Nick, I’ve heard of red/green color blindness, but not blue/white color blindness.
Posted By: crash Re: What's Wrong With This Picture? - 02/27/04 01:17 AM
While we are on the topic of transfer switches, I have a question. What is an overlapping neutral, and how does it differ from a switched or solid neutral? I apoligize if I am a bit off topic, but in trying to figure out this picture I came across the term "overlapping neutral".
Posted By: n1ist Re: What's Wrong With This Picture? - 02/27/04 02:45 AM
I can't tell who makes that switch but it looks a lot like an Asco. In that case, the source and load lines are going to right places. I couldn't find any info on the neutral assembly, but if that's a switch, isn't the load tied
to the generator position?
Posted By: Nick Re: What's Wrong With This Picture? - 02/27/04 02:53 AM
OK, here's the deal. Yes the generator feed is not there yet. But if you look at where the grounded conductors land when the generator feed is terminated, the grounded conductor will land on the lug in the middle. The load conductors are landed on the top lugs and the utility feed is landed on the bottom lugs. Even looking up close at the markings on the switch this appears to be correct. Well, it wasn't. The load neutral (grounded conductor) should have been landed on the lug which, in the picture, is empty. This switch feeds an article 700 lighting panel which we used as areas were complete, for lighting during construction. But wait! [Linked Image] How did the thing work without the grounded conductor on 277V lighting loads!? That was the $100K question when we found the switch was terminated wrong. ([ side bar.... We found there was a problem when mounting exit lights. The guys were saying they were getting sparks from neutral to the boxes and it was enough potential to register on a tick tracer. We promptly investigated and found this problem /side bar]) We were too pressed for time to investigate then but found out what happened a few weeks later when tracing another problem. There was a bathroom area that remained intact from the original building that we just had to add some down lights to. Well, a janitor closet in that area stayed hot when the circuit feeding it was shut down. Hmmm [Linked Image] Well, something is tied together right? But the emergency circuit in the area is C phase and the normal power is A phase. They would have tripped right. Wrong! The original building was phased yellow, orange, brown. All our new stuff was installed a more conventional (and per spec) brown, orange, yellow. The emergency system was new and the normal power panel was an existing feeder. So, yes the circuits were tied together in a box above the restrooms where we tapped into the existing conduit system. (The guy that made it up was gone so we couldn’t even chastise him [Linked Image] ) So thinking back to the transfer switch problem this explained why we didn’t see a problem when it was initially energized! The two circuits from different systems being tied together created a path for current to flow back to its source. All emergency power circuits couldn’t go the correct path but it found it’s way from the neutral bus in the panel, back to the box on the other side of the building where the foul up was (via that circuits neutral) back to the main gear via the normal power circuit and feeder! Kind of a comedy of errors don’t ya think? Boy do I love fast track remodels! [Linked Image]
Posted By: Nick Re: What's Wrong With This Picture? - 02/27/04 02:54 AM
n1ist,
You got it!!!

BTW: Its a Kohler switch. They use ASCO internals So it's really an ASCO switch in a Kohler enclosure.

[This message has been edited by Nick (edited 02-26-2004).]
Posted By: Nick Re: What's Wrong With This Picture? - 02/27/04 02:57 AM
Crash,
An overlapping neutral is a make before break contact. In other words the connection from the normal source is not connected until the emergency source makes contact and visa versa.
Posted By: crash Re: What's Wrong With This Picture? - 02/27/04 03:46 AM
Thanks for information Nick. Your picture sparked my curiosity on neutrals in transfer switches. I had been under the impression that all the neutrals were always bussed together in transfer switches.
Posted By: electure Re: What's Wrong With This Picture? - 02/27/04 12:45 PM
While, they've got it apart, Nick, they probably should slip some bushings on those connectors...S
Posted By: pauluk Re: What's Wrong With This Picture? - 02/27/04 02:29 PM
On the load conductors running into the top terminals, wouldn't it also have been a good idea to leave a little extra slack in them to allow for any future re-terminations?
Posted By: rmiell Re: What's Wrong With This Picture? - 02/27/04 04:58 PM
And shouldn't the emt connectors have grounding bushing on them, since this over 250volts to ground?

Rick
Posted By: Nick Re: What's Wrong With This Picture? - 02/28/04 12:02 AM
Scott,
The connectors are insulated throat.

Paul, Yes but it looks so much better this way. [Linked Image] (Actually there is slack on the switchgear side of the line feed and there is a pull box just out of site on the load side with a small loop.)

Rick,
Ground bushings not required. All three conduits are in clean KO's.
Posted By: electure Re: What's Wrong With This Picture? - 02/29/04 05:45 PM
Boy, Nick
You guys sure get the neatest material.
Colored wire in the larger sizes and everything [Linked Image]...S
Posted By: Bjarney Re: What's Wrong With This Picture? - 02/29/04 09:10 PM
Is it my imagination, or does it look like Cø and N {blue/white} are flopped on the upper and lower sides of the switch?
Posted By: Nick Re: What's Wrong With This Picture? - 02/29/04 09:17 PM
Scott,
This is the first job I used the colored wire on. I had some problems with the way the manufacturers marked it so I not sure I will use it again until the perfect the marking process.
Bjarney,
Check your display settings. The wire colors in the picture are brown, orange yellow and grey. [Linked Image]
Posted By: Scott35 Re: What's Wrong With This Picture? - 03/03/04 11:05 AM
Man, those Colored (other than Black) Conductors look SWEET!!!

At first, I thought that Nick had the art of Colored Tape Wire Wrapping down to a Genius level!!!

These are like size 3/0 or 4/0 AWG, aren't they?
At least they appear to be >#2...

What's the price difference and availability of B.O.Y. + Gray colored Insulation sized >#1 AWG / vs / Plain-old Black Insulation?

I Assume (read "Ass-U-Me") the colors of Red, Blue, Violet/Purple, White and Green are also available.

If the price is right and available in a reasonable time, might consider using on future projects!

Scott35.
Posted By: Nick Re: What's Wrong With This Picture? - 03/06/04 01:42 AM
Hey Scott,
The colored wire in the picture is 350 Kcmil. Yes it is available in all colors and allot of the major suppliers are stocking it now. Price is about 5 to 10% more that regular black insulation. There is some labor cost savings in all the time you don't have to spend identifying wire during and after pulls and possible cross phasing mistakes. You have to look at the job and decide for yourself if it's worth it.
This is the first job I tried it on because the shop was pushing it. I had a few problem with on particular manufacturers method of making the insulation though. It was non existent! They had to come out to the job and mark the wire, write letters to the city etc... What a mess. I am assured they have fixed the problem however. [Linked Image]
Posted By: Bjarney Re: What's Wrong With This Picture? - 03/06/04 02:33 AM
Nick, apologies for my old monitor. It looked like blk-red-wht-blu {versus blk-red-blu-wht} here... er, sorry, B-O-Y-Grey.

But real colored 350kcmil!?! Cool.




[This message has been edited by Bjarney (edited 03-05-2004).]