Posted By: Admin Hot Transformer !! - 08/19/03 11:29 PM
[Linked Image]
Quote
This transformer was marked that it needed 6" air space front and rear.

It is heavily loaded 24/7 and the top was to hot to touch.

It was pushed back tight to the wall.

Bob (iwire)
Posted By: Bjarney Re: Hot Transformer !! - 08/20/03 12:18 AM
Understand that {economy} dry-type transformers are often rated at 150°C rise—which means the hottest part of the transformer can run 270°F above room temperature at rated load. Hence, the logic behind the labeled clearance requirement.