Posted By: Admin Is this Code compliant? - 12/30/01 11:29 PM
[Linked Image]

Is this installation Code compliant?

- Electure
Posted By: Joe Tedesco Re: Is this Code compliant? - 12/30/01 11:57 PM
In addition to lack of proper workspace in front of the disconnect covered by Article 110 the following rule is also violated.

Was this another one that fell through the $$$ cracks?

440-14. Location
Disconnecting means shall be located within sight from and readily accessible from the air-conditioning or refrigerating equipment. The disconnecting means shall be permitted to be installed on or within the air-conditioning or refrigerating equipment.
Posted By: George Corron Re: Is this Code compliant? - 12/31/01 12:03 AM
I believe you would also find that ALL the mounting holes must be covered to keep the 3R rating of the disconnect.
Posted By: Nick Re: Is this Code compliant? - 12/31/01 01:03 AM
Will the cover even open?!
Posted By: electure Re: Is this Code compliant? - 12/31/01 06:23 PM
The cover will open all the way.

So, does this qualify as a piece of equipment that will be "likely to require examination, adjustment, servicing, or maintenance while energized" per 110.26(A)?
You've got to shut it off to open the cover.

(George wins the prize, it already has some evidence of water damage inside. One good El Nino winter and it's history)
Posted By: Redsy Re: Is this Code compliant? - 12/31/01 11:21 PM
electure,

I would say 110.26(A) applies. You might need to check incoming voltage.