Posted By: Admin Crowded J-box - 01/14/01 12:58 AM
<p align="center"> <img border="0" src=&q...uot;400" height="258">

Click on Photo for a Closer Look
<p align="center">Submitted by Virgil Kelly (aka sparky66wv)

"
This is of a new J box that's over crowded and hard to get

an extension on, though I succeeded with some work"
Posted By: sparky Re: Crowded J-box - 01/14/01 01:51 PM
Looks like that pipe & coupling are in the way there....
Posted By: Tom Re: Crowded J-box - 01/15/01 10:43 PM
I see that there are no box offsets in the EMT. I realize they aren't required, but that is definitely poor workmanship. That looks like type MC cable, if it is, was there a connection from the box to all the equipment grounds?
Posted By: sparky66wv Re: Crowded J-box - 01/16/01 12:12 AM
Yes, there was a grounding conductor in the box (from the panel) that was attached to the MC grounding conductors and pigtailed to the box. This was above a suspended ceiling so I can overlook the lack of offsets. The only error was over-crowding the box. Personally, I don't buy any J-box smaller than a 4"x4"x2-1/8".