Posted By: Admin Water Pipe Location - 10/25/03 03:48 AM
[Linked Image]
Quote
Is it a violation for a water pipe to be under the equipment here?

Joe
Posted By: resqcapt19 Re: Water Pipe Location - 10/25/03 03:49 PM
While there is not a violation of the safety work space required by 110.26(A), there is a violation of the "dedicated equipment space" required by 110.25(F)(1)(a).
Don
Posted By: iwire Re: Water Pipe Location - 10/25/03 08:31 PM
I am wondering about what looks like the use of parallel conductors smaller than 1/0?

Bob
Posted By: ThinkGood Re: Water Pipe Location - 10/26/03 12:21 AM
Quote
Is it a violation for a water pipe to be under the equipment here?

Or is the violation having the equipment over the water pipe?
Posted By: mvpmaintman Re: Water Pipe Location - 10/29/03 12:55 AM
I think a bigger problem might be the pipe above the panel from the looks of the rust on the outside of the panel and the trough under it. I popped a cover on one like this once and found two of the three fuses in the main rusted into the holders.
Posted By: Knightelectrical Re: Water Pipe Location - 10/31/03 04:37 AM
Lots of problems here. Are those the right kind of straps, look like one hole EMT straps to me.
334.15 B (NM cable?) "shall be protected" is not met.