Posted By: bigpapa 0-10V dimmer conductors - 08/16/15 03:23 AM
Can we do this?
The low voltage wires for 0-10V dimmer controls end up in the same enclosure as the power conductors at the dimmer and at the light fixture. I don't see any reason they can't be in the same conduit.
Any comments appreciated.
Posted By: twh Re: 0-10V dimmer conductors - 08/16/15 06:06 AM
I think the rule is that all conductors must have insulation rated for the highest voltage.
Posted By: HotLine1 Re: 0-10V dimmer conductors - 08/16/15 08:54 PM
First, from stateside, what do the installation instructions require??

Second as twh said, down here the insulation must be all rated at the highest available voltage in the conduit/enclosures.

Posted By: bigpapa Re: 0-10V dimmer conductors - 08/17/15 06:05 AM
These will be Sensorswitch nLight dimmers packs which I have never worked with.
I was curious of the code implications, but I'm thinking a shielded cable of some sort should work as long as it has the proper voltage rating.
Guess as a last resort I can read the instructions.
I have a #14 MC cable in place as a backup just in case there is an issue but still, running in the same conduit would be easier.