Posted By: Potseal Terminating individual bonding conductors - 01/08/14 05:32 AM
I looked in the code book for a rule that states that you have to terminate individual bonding conductors for each circuit in the distribution panel. Other than "patient care" areas I could not find such a rule.

For example, what if you had 15 - #12 bonding conductors to be terminated in a distribution panel but instead of bringing them to the panel you terminate them on a common termination strip in a D-box just before the panel then come off the same common termination strip with 2 - #6 bonding conductors which you then terminate in the panel? Is there any rules that oppose this? The only reason I would consider this is due to the lack of space in the distribution panel and wanting to cut down the number of wires coming in.
Look at 2011 NEC 300.3(B)Page 70-135.
Originally Posted by Yoopersup
Look at 2011 NEC 300.3(B)Page 70-135.


We use the Canadian electrical code . some year we may be harmonized with the NEC.