Posted By: MJ2000 Swimming pool water heater - 04/30/12 02:59 AM
Does swimming pool water heater need to be protected with
GFCI breaker (50A)?
The heater(heat pump) is more than 10' from the pool.

Thanks
Posted By: leland Re: Swimming pool water heater - 05/01/12 02:43 AM
Mj.
In the States,the pool heater does not need to be GFCI. (2008- NEC) 680.9

680.26(6)(b). bonded and grounded per/instructions.

Posted By: MJ2000 Re: Swimming pool water heater - 05/01/12 03:54 AM
Even if the code doesn't require a GFCI breaker, is it still worth the extra $100 for better protection?
Posted By: HotLine1 Re: Swimming pool water heater - 05/01/12 03:09 PM
MJ:

IMHO, I would install GF protection. I don't have any CEC info for you.

An explanation of the benefits to the client, as opposed to the $$ for GF should help if the job costs are considered to be costly.
Posted By: mikesh Re: Swimming pool water heater - 05/03/12 01:02 AM
Well the heater leaks current and a class A gfci won't even hold if the heater is large enough. Class b GF protection does not protect life so how can it work for life protection except that class b can be used where class a is not available? Actually look at rule 68-068 especially subrule 7
So if the heater is within 3 meters and not the other side of a wall then yes GFCI protection is required. If the heater is further than 3 meters then no.