Hello,
I work in a firm that build plants to do the concrete.
Usally we use to wire ours motors/sensors to the panelboards a type of cable named tray cable exposed run (TC-ER) UL LISTED.
If I need to buy a festoon cable for a particular section of the plant which kind I should purchase? Which specifications should have? Exist a TC-ER festoon cable?
Thank you.
You should be looking for something similar to this.
http://customcable.thomasnet.com/vi...rop-cable-duplex-triplex-and-quadruplex.If this is inside, be sure the insulation is rated to be used inside. (smoke and flame)
Where do you intend to use the wire (country)? In Germany I think you'd likely use NYMT if not exposed to direct sunlight, or NYY fastened to a steel cable.
I'll install this cable in Canada with 575V/3phase feeding.
I need to know if there is an article in the NEC about this kind of cable.
I should feed a trolley bucket. Do you have an idea how to do? usually we use TC-ER cable....about the festoon cable??
The NEC does not apply in Canada, that is a issue for the CEC, Canadian Electrical Code.
Ah...!!!You're right!!
However, meanwhile I wait to find CEC, someone could please help me??
Since, I couldn't consider my plant as a machinery but as a building, i.e. a group of panelboards wired together.
Which kind of cable I need for an industrial control equipment?
Which kind of cable I need for trolleys?
Thank you in advance!!!
please...someone could help me???
http://customcable.thomasnet.com/vi...oon-cable--50-c-to-90-c-ul-and-csa-600v?For control
Similar type for Power. in fact many of these cables are available in #2 or larger
anywhere from 10 #16 control wires to 4 #2 power wires