Hi guys,
I need an explanation for the ESA09 Rule 02-034.

Thanks
Posted By: brsele Re: Rule 02-034 - 02/23/10 05:56 PM
Don't throw an electric fan into a bathtub in an attempt to create a jaccuzi.
Posted By: mr_electrician Re: Rule 02-034 - 02/23/10 06:27 PM
Not sure what your getting confused on? I agree with brsele. You could also say Rule 2-034 means not to use steel conduit as a replacement for copper conductors!!!
Posted By: MJ2000 Re: Rule 02-034 - 02/23/10 11:35 PM
I didn't post this topic as a joke. I couldn't find this rule in the Code book.The problem is that I got this in the Notice of Deficiency from an inspector and an explanation for this rule is "Panel covers shall be installed.
Posted By: dougwells Re: Rule 02-034 - 02/24/10 12:58 AM
were panel covers missing ?? you really have not explained much here.
I am in BC and that rule is not in the CEC. what does it say in the ESA
Posted By: Eddy Current Re: Rule 02-034 - 02/24/10 01:09 AM
2-034 Use of approved equipment
No person shall use electrical equipment for any purpose or in any manner other than the purpose or manner for which it is intended.
Posted By: dougwells Re: Rule 02-034 - 02/24/10 01:20 AM
Thanks smile
Posted By: mikesh Re: Rule 02-034 - 02/24/10 06:58 PM
If the inspector said panel covers shal be installed i would think he might quote 2-202 or other rule from 2-200.
Cover on or off, i am assuming the panel was being used as a panel?
Posted By: MJ2000 Re: Rule 02-034 - 02/25/10 04:30 AM
* Two screws missing from the panel cover

It could be reason for that notice, but it has been for long time!