Posted By: Oh Well joints in a panel - 09/22/08 05:44 PM
Is it acceptable in Canada to make joints using wire connectors in a beaker panel? Thanks in advance
Posted By: brsele Re: joints in a panel - 09/22/08 09:28 PM
Originally Posted by Oh Well
Is it acceptable in Canada to make joints using wire connectors in a beaker panel? Thanks in advance


Yes
Posted By: Sixer Re: joints in a panel - 09/23/08 01:48 PM
Can you give a rule number for this?
Posted By: mikesh Re: joints in a panel - 09/24/08 04:16 PM
6-212 says no but 12-3032 says you may on a retrofit up to %75 of the area.
So what applies? You can't splice in the service according to 6-212 but can if you are adding to an existing installation? Either way you can't do it in a new installation. Have both rules at hand when you speak to the inspector.
From this jurisdiction we would not allow splices in the service entry section of a combination panel or switch.