CEC rule 10-106 (2) where it states wiring systems supplied by an ungrounded system shall be equiped with a suitable ground detection device to indicate the presence of a ground fault.
How is this accomplished and what constitues a suitable device
thanks
The device is a "ground fault indicator panel". I got one from Eecol a while ago. Willet, in Estevan, Saskatchewan, makes them.

It is three transformer type panel lights. Each is connected betweeen a phase and ground. The indication is that, in the event of a ground fault, one light goes out and the other two get bright.

You can't make your own, though. It wouldn't be CSA approved.
Im looking at an FPE GIL-600 I guess i'm asking where it would connect to the system.
thanks http://www.schneider-electric.ca/www/en/products/ground/html/gil.htm


[This message has been edited by frank (edited 11-27-2006).]
Simply take it off the splitter, as you would any other load. Make sure it has a fused disconnect too.
One of the systems feeding the plant where I work is a three phase ungrounded 240V Delta system. The ground fault indicators are feed directly from the load side of the main circuit breaker. (This is an old plant circa 1930's )

The ground indicators are just three bulbs connected in a wye arrangement with the centre point connected to ground. Under normal conditions all three lamps glow dimly and at equal intensity. If one phase becomes grounded the two lamps on the ungrounded phases glow brightly (they now see a full 240V) and the lamp on the grounded phase goes out. Pretty simple but it works well.